I am having an additional mains spur installed in my house. It will only be feeding a single double wall socket and will be connected to a 32A RCD within a mains consumer unit.
I've been told that I can not use an unswitched wall socket as "each circuit must have a switch".
Is this correct? All items that will be connected to these sockets have internal fuses (as do the mains leads), so is it dangerous using an unswitched socket?
Thanks.
Back to the original question. You can use an unswitched wall socket.
However for a single double socket use a 20A RCD not 32A. A double socket is rated at a lot less than 2 x 13A. Also using a 20A RCD allows it to be wired in 2.5mm cable rather than 4mm.