Would it be possible to fit an Unvented Hot water Cylinder off a Combi Boiler (both in loft) just to supply a bath and shower? I could zone of the cylinder from the heating side so only heating this Cylinder when hot water is req from it?
Would it be possible to fit an Unvented Hot water Cylinder off a Combi Boiler (both in loft) just to supply a bath and shower? I could zone of the cylinder from the heating side so only heating this Cylinder when hot water is req from it?
unvented cyls need a 2 port spring return valve so a 's plan' not a 'y plan' should be used.You can wire a standard y or s plan system
true, but that confuses a lot of people.Nothing wrong with a 'Y' plan, but you will have to fit the supplied 2 port as well on the hW flow to the cylinder
Would it be possible to fit an Unvented Hot water Cylinder off a Combi Boiler (both in loft) just to supply a bath and shower? I could zone of the cylinder from the heating side so only heating this Cylinder when hot water is req from it?
Fitting an unvented cylinder to supply water to washing areas and existing combi to supply hot water to kitchen gives you best of both worlds.
Can BB explain how he connects the cold water into this system he is recommending? I can't see why, when the cylinder is cold, the hot water from the combi isn't blended with mains cold and is therefore swamped with cold.
Lastly, some combis would not tolerate the high temperature recirculated water coming in their cold input.
Can BB explain how he connects the cold water into this system he is recommending? I can't see why, when the cylinder is cold, the hot water from the combi isn't blended with mains cold and is therefore swamped with cold.
It is plain you can't understand something so simple. The cold feed to the cylinder is at the bottom, us usual, and the DHW draw off is at the top, as usual. The combi acts like a pumped circulator only. It only comes on when the cylinder thermostat calls for heat and the bronze pump kicks in.
Can BB explain how he connects the cold water into this system he is recommending? I can't see why, when the cylinder is cold, the hot water from the combi isn't blended with mains cold and is therefore swamped with cold.
It is plain you can't understand something so simple. The cold feed to the cylinder is at the bottom, us usual, and the DHW draw off is at the top, as usual. The combi acts like a pumped circulator only. It only comes on when the cylinder thermostat calls for heat and the bronze pump kicks in.
Can you post a simple drawing of this BB, showing the pipe connections inparticular the cold mains connection.