Glad to see you maintained the correct phase colours.
Glad to see you maintained the correct phase colours.
A lot of sound guys will categorically refuse to use different phases 'because it will create interference'.There are alot of 'old wives tales' and other myths passed down through the generations about the 'dangers' of kit powered from different phases. Not least within the BBC of all places. In my 'former life' of power generation & distribution in the entertainment business I've had several heated discussions with quite senior Engineers about powering OB trucks. Historically all TV OB gensets where single phase. OB trucks were configured to take in multiple feeds (eg. technical, Hotel & Air con) which it was clearly stipulated must all be on the same phase. Indeed the input panels often had neons wired between the phase pins of the (often 63 or 125A) ceeforms to detect if the supply was truely single phase or two phases from a 3 phase supply.
When questioned about this the Engineers would often get very defensive insisting that such a power scheme would lead to 415V on the interconneting cables of equipment & its ultimate destruction. Even after explaining that such a scenario would require at least a double or even triple failure combined with a bad earth they still insisted that the supply be true single phase. Even powering different OB trucks from different phases was frowned upon (same argument... the interconnecting cables between the trucks would join together two pieces of equipment that had 415V between them). Even after explaining that for that to be so the interconnecting cables would have to be at phase potential above earth ... ie. the equipment had already catastrophically failed.
I suppose that that might well be true, unless one has good balance over the three phases and all running in the same cable.A lot of sound guys will categorically refuse to use different phases 'because it will create interference'.
A lot of sound guys will categorically refuse to use different phases 'because it will create interference'.
It is not a problem I have encountered, as long as the audio system is designed and installed correctly, ie see post #49I suppose that that might well be true, unless one has good balance over the three phases and all running in the same cable.
Kind Regards, John
Yes, I can believe that - but it does depend upon the audio stuff being designed/constructed to be fairly immune to 50Hz fields - since there would presumably be plenty of that in the vicinity of a 3-phase cable carrying fairly high and unbalanced currents.It is not a problem I have encountered, as long as the audio system is designed and installed correctly, ie see post #49
Why would the cable be unbalanced?Yes, I can believe that - but it does depend upon the audio stuff being designed/constructed to be fairly immune to 50Hz fields - since there would presumably be plenty of that in the vicinity of a 3-phase cable carrying fairly high and unbalanced currents.
Kind Regards, John
I suppose it wouldn't - if it had a neutral.Why would the cable be unbalanced?
Even without a neutral the 3ph cable will be balanced, or else the RCD would trip.I suppose it wouldn't - if it had a neutral.
Kind Regards, John
Eh? I'm talking about between-phases balance (something which is by no means always the case). A 3-phase RCD will only trip if the vector sum of the three phase currents is different from that in the neutral.Even without a neutral the 3ph cable will be balanced, or else the RCD would trip.
The RCD doesn't know, or even care, what the selection of conductors are that it's monitoring. If there is no leakage, to earth or otherwise, then the resultant summed current in the cable will be zero regardless of how balanced the phases are, and the resultant magnetic field around the cable will be [relatively] minimal.Eh? I'm talking about between-phases balance (something which is by no means always the case). A 3-phase RCD will only trip if the vector sum of the three phase currents is different from that in the neutral.
Even if current is flowing in only one or two of the three phases (i.e. extreme cases of phase imbalance), provided nothing is leaking to earth, a 3-phase RCD will still not trip.
Kind Regards, John
Yes, but as I implied, the vector sum of currents in all the conductors will be zero only if either (a) all three phase and neutral conductors are in the cable or (b) if, when there is no neutral conductor in the cable, currents are identical in the three phase conductors (i.e. perfect phase balance).I'm referring to the total current flow in every conductor in the cable. If there is no leakage, to earth or otherwise, then the resultant summed current in the cable will be zero regardless of how balanced the phases are.
The time I'm wary of big fields is the main singles coming away from the generators, sometimes they are just a random heap or spread out over a wide area.
As I understand it you are referring to a complete power line in one cable, ie it contains all of the current carrying conductors in a circuit. In this situation the CABLE will be carrying a balanced load regardless of how many phases are loaded, the RCD will be happy and there will be minimal magnetic field.Yes, I can believe that - but it does depend upon the audio stuff being designed/constructed to be fairly immune to 50Hz fields - since there would presumably be plenty of that in the vicinity of a 3-phase cable carrying fairly high and unbalanced currents.
Kind Regards, John
Indeed, but when I wrote that the cable would only be balanced if it does contain "all of the current carrying conductors in a circuit" (i.e. including a neutral - I wrote "if it had a neutral"), you responded with ...This is the quote I have been referring to ..... As I understand it you are referring to a complete power line in one cable, ie it contains all of the current carrying conductors in a circuit. In this situation the CABLE will be carrying a balanced load regardless of how many phases are loaded, the RCD will be happy and there will be minimal magnetic field.
Which I'm afraid I did (and still do) struggle to understand.Even without a neutral the 3ph cable will be balanced, or else the RCD would trip.