If that's a 20C dT per zone you get:
Zone 1: Flow = 75; Return = 55
Zone 2: Flow = 70; Return = 50
Zone 3: Flow = 65; Return = 45
Zone 4: Flow = 60; Return = 40
If it's a 20C deltaT at the boiler then it's a different game. I'm still working on that one.
Obviously I was referring to the primary flow temp after it passes each zone , your still working on it?
75c flow temp.
Total flow rate = 0.95 l/s (80kw)
Zone flow rate = 0.238 l/s (20kw).
1st zone calc.......
(0.72 x 75) + (0.23 x 55)/0.95.