is the boiler wired up via a standard wiring centre or a Vaillant VR61/65?
See my earlier post (below) as you have not yet provided the info:-How can I check and prove that the boiler is getting the 20l/min required?
With the Vaillant controls fitted you can have different max kW values for CH (d.0) and HW (d.77). However, this will not make any difference in your situation as you have effectively down rated the HW via d.0 to 11kW already.Did you make a note of the D.41 values? I'm particulary interested in the delta T (i.e. the difference between D.40 and D.41) on the initial burn phase and what it was at the point it switched off at 6min 54 seconds in to better understand what the boiler was doing?
This information will also enable the calculation of flow rate through the boiler.
I could hear the boiler go quieter at 50 seconds when it takes onboard the 11kw setting and you can see from the measurements that the boiler had reduced output at this point
UpgradeME: checked a 2007 418 yesterday and it was doing (D.33) 258 for initial 45-50 secs, then rising to 410 (18kw). I took that to be 63% actually I'm not sure where I got 75% from. Maybe have a look at yours and see if there's any difference with BMU releases possibly. D.0 setting made no difference..