Vaillant Turbomax 282e diaphragm

I have been reading all this for a bit of fun.

But I am surprised that no one mentioned what I have always done and thought was standard practice.

That is to start at zero HW flow and SLOWLY increase it until boiler turns on, then to stap and measure the flow rate and compare it with the maker's spec!
 
Sponsored Links
There are a few other boiler checks that need looking at including airflow..and unfortunately it's beyond diy.
 