doitall said:
There's a hundred quid to a charity of your choice say it pumps over
OK DIA, you'd better get the cheque book out. I'll let you choose the charity (ARGI?) since it's your money.
The pumping over question is easily answered by a simple calculation as follows:-
1. Output of Viessmann boiler is 22.3kW (=22.3 kJ/sec). Temperature drop across system should be 20°C. Specific heat of water at 70°C is 4.190 kJ/kg.
2. The flow of water around the main circuit will therefore be 22.3 / (20 x 4.19) = 0.27 kg/sec.
3. Head loss in 22mm pipe with 0.27 kg/s flowing is around 40mm per metre run (from tables).
4. Preferred distance from vent connection to feed connection (neutral point) is less than 150mm, but allowing for Viessmann drawing which suggests larger gap (another mistake!), let's call it 1 metre (equivalent length) to be generous to you.
5. Therefore water level in vent pipe will be
40mm above level in feed tank. (Or only 6mm if we take the 150mm figure referred to above)
4. It's clear from the Viessmann drawing (and standard practice) that the vent pipe invert should be well above the water level in the feed tank - but let's assume this is only 200mm (I'm feeling really generous).
5. 40mm is less than 200mm, therefore no pumping over, therefore your bank account is less £100.