Do you mean that the user can set a minimum and maximum fan speed? I'm asking because the OP seems to have a problem where the power never goes below 23% and I'm wondering if inadvertently the minimum fan speed has been set to 23%.
Not on FB
All I can see is set Max output as a %
As far as I can tell when I see modulation 100% means no modulation I've seen it when using dhw some times
This is today's modulation history so 19 hours and the burn times
View attachment 298359
View attachment 298358
The burner on periods are very low compared to the off periods, looks like the flowtemp shoots up to SP+trip hysteresis and then takes a long time to get the flowtemp down enough to refire the boiler so must be using a very low flowrate (if no anticycle).What does the Y axis represent on the burner on graph?
There seems a 9⁰C ∆T on F&R which o think is good on a low temp system.
I mentioned FB as there are groups of Viessmann installers on there very knowledgeable who have confronted these issues before and may be able to help.
Just re-reading earlier posts. The control will be fitted to system or combi boilers, that's why there's a DHW schedule, we do the same.So it's been a bit better I'm now on a curve of .5 and +5
One thing I don't understand is why there is a dhw schedule on a combi? Also is there anything I can tweak to speed up the switch to dhw? It takes a bit too long for the Mrs to be happy
10% output should be either 3.2kw or 2.7kw if the max CH output is 85% of HW output.Max output at 10% has made no difference to modulation amount really and burn time is up slightly first one was 10 minutes the next was down to 8