Still trying to figure out why the radiators were not heating up on the scheduled program time.
I've adjusted the programs for the DHW to start and finish 6am - 840am and the CH to start 06:40am - 9am.
I am assuming that 40 mins should be enough for the cylinder to be warmed up as this is given priority I was told.
Provided the boiler doesn't wake you up, why not bring it on earlier? There is then less chance of it clashing with the CH.
We had been finding at 20c the radiators were not getting warm for at least 45 mins or so and even then they were only slightly warm.
So room temp was increased to 25c now I am gradually bring temp down 2c a day.
Will try curve at 2 once temp testing had been completed.
Temp testing is a waste of time as the "thermostat" is not measuring the room temperature, it's just shifting the curve up and down, parallel to the standard curve, i.e the slope stays the same. As I said previously, leave the "stat" at 20 and change the curve to 2. If the house still doesn't reach 20, increase the curve and vice versa.