I have been out to look at a problem in a commercial property with time limited access due to the nature of the site.
Very simple circuit: single 30A Wylex fused switch containing yellow 20A fuse feeding:
A DSSO in adjacent building with 4mm² T&E guess 15m.
A DSSO in adjacent room with 2.5mm² T&E guess 4m.
While decorating the room the steam wallpaper stripper didn't work but a LED table light does (no surprise).
Extension lead from same circuit from the other building runs the steamer.
My initial suspicion being the socket or plug, tried with their kettle (most common load in other building) and confirm report so fitted a different socket - no change.
Access to fusebox is difficult due to security and a long treck round the building and grounds (300-400m) but can get fusebox switched on/off with ease via phone call.
Switched off I can see open circuit between L & N & E (3 tests) at both sockets, shorting L & N at either socket shows a short circuit at the other. but this is only using a multimeter.
A colleague has been in tonight and confirms symptoms, even swapped sockets over. Couldn't get access to fusebox and repeated tests between sockets using a KEW MFT: L-N loop and L or N - E loop. He didn't send the results other than 'spot on' (second image)
I think this is all it is:
Now waiting for a time for two of us to go in.
Any ideas?
Very simple circuit: single 30A Wylex fused switch containing yellow 20A fuse feeding:
A DSSO in adjacent building with 4mm² T&E guess 15m.
A DSSO in adjacent room with 2.5mm² T&E guess 4m.
While decorating the room the steam wallpaper stripper didn't work but a LED table light does (no surprise).
Extension lead from same circuit from the other building runs the steamer.
My initial suspicion being the socket or plug, tried with their kettle (most common load in other building) and confirm report so fitted a different socket - no change.
Access to fusebox is difficult due to security and a long treck round the building and grounds (300-400m) but can get fusebox switched on/off with ease via phone call.
Switched off I can see open circuit between L & N & E (3 tests) at both sockets, shorting L & N at either socket shows a short circuit at the other. but this is only using a multimeter.
A colleague has been in tonight and confirms symptoms, even swapped sockets over. Couldn't get access to fusebox and repeated tests between sockets using a KEW MFT: L-N loop and L or N - E loop. He didn't send the results other than 'spot on' (second image)
I think this is all it is:
Now waiting for a time for two of us to go in.
Any ideas?