I think that probably says is all.In real terms with 45 years in the trade that was the only time I found something would not work simply because of volt drop.
Kind Regards, John
I think that probably says is all.In real terms with 45 years in the trade that was the only time I found something would not work simply because of volt drop.
I think that probably says is all.In real terms with 45 years in the trade that was the only time I found something would not work simply because of volt drop.
Kind Regards, John
Good to see you. What is says to me is that, for virtually all practical purposes (in domestic installations, which is what this site is meant to be about), VD is not something one needs to be concerned about.Out of interest, what does this say to you?
Well, as you know, that's not allowed, so I presume you meant 216.2V.And what if they start with a supply voltage of 204.7V?
You highlight another anomaly with all this interest in VD within an installation. Consider a supply with an external L-N loop impedance of 0.35Ω and a "40A shower". The voltage at the shower will then fall by 14V (aka ~6%) when the shower is switched on, even if the final circuit introduces minimal additional VD (i.e. very short and large CSA).As I said before I looked into the measuring of volt drop. To measure we need to measure voltage with and without a load. ... So to start with we need two readings, one for the supply impedance and one for the end of circuit impedance. Taking one from the other we have the impedance so looking at a ring final as an example.
We should strap some magnets to Hr. Dr. Ohm, and wrap some copper wire around his coffinNot sure I am following that,
Where did the 100A come from?max volt drop at the head is 6% i.e. with the full permitted load. At one time I would have assumed no load at transformer voltage would be at max i.e. plus 10% however with micro generation that's really no longer an option so let us assume 251.2 volt at transformer no load giving just a little leeway, so at 100A they are allowed a 35 volt drop so the maximum impedance will be 0.35Ω. Oh where have I seen that figure before?
Another thing you also said was that you didn't follow the argument that, at whatever voltage was present at the service head, if you whack another 40A load onto the cable that voltage will drop.Your saying a 100A supply with a 0.35Ω impedance would have a max volt drop of 35 volts, which is exactly what I also said.
Did I? I was assuming potential volt drop. The volt drop that would happen if the circuit was loaded to it's maximum. So add another 40A and the potential volt drop is 230 volt. In other words the protective device has tripped so there is no voltage.Another thing you also said was that you didn't follow the argument that, at whatever voltage was present at the service head, if you whack another 40A load onto the cable that voltage will drop.Your saying a 100A supply with a 0.35Ω impedance would have a max volt drop of 35 volts, which is exactly what I also said.
Indeed, if one had a total installation load on the installation (with the shower on) of, say, 60A, an external L-N impedance of 0.35Ω and the 'permitted' 5% VD in the shower's final circuit, then, if were were unlucky enough to start with the minimum permitted supply voltage (216.2V), then the shower would only be getting about 184V.
There may be no load in your house but if there is a load next door and you at the end of along feeder then the supply to your property will drop significantly.What John seemed to be implying was we could have a voltage of 216.2 with no load.
I'm rather confused, because there is a lot which doesn't seem seem right about all this....Not sure I am following that, max volt drop at the head is 6% i.e. with the full permitted load. At one time I would have assumed no load at transformer voltage would be at max i.e. plus 10% however with micro generation that's really no longer an option so let us assume 251.2 volt at transformer no load giving just a little leeway, so at 100A they are allowed a 35 volt drop so the maximum impedance will be 0.35Ω. Oh where have I seen that figure before?