I haven't had a chance for more than a cursory glance as yet, but this network design manual from one DNO appears to have some interesting information:
http://www.eon-uk.com/downloads/network_design_manual.pdf The introductory notes plus the section on LV distribution and voltage regulation might prove interesting.
Thanks - there's a lot of reading there. Watch this space (probably for a while)!
Right ... for starters .... The formulae for calculating VD in sections of an LV main (section 6.1.2 of document) are pretty confusing ....
Goodness knows what ‘L’ is. I suspect that it’s probably the length of the section, with Rp being the Phase Resistance
per metre (not just “Phase Resistance”, as defined).
More confusing is that whilst they define Rn as being Neutral Resistance, it does not appear in any of their expressions! However, their calculations of VD boil down, as expected, to “resistance times current times various correction factors”, and one of those correction factors (F1, “Unbalance Correction Factor”) becomes 5.14 for a single consumer/ service (i.e. no ‘looping’) situation. Hence the VD calculated by multiplying current by just the Phase resistance then gets multiplied by 5.14! The other correction factors (Diversity Correction Factors) reflect the fact that one can rely increasingly less on the concept of diversity as the number of connected consumers decreases - the calculated VD increases quite rapidly if the number of connected consumers (I presume across all 3 phases) falls below about 12. I presume that the (“a/3”) reflects the fact that they are talking about the usual situation in which the loads of the total number of connected consumers are spread across the three phases.
Whatever, these calculations are obviously crucially dependent on the statistical concept of diversity. As we’ve discussed before the ‘After Diversity Maximum Demands’ (ADMDs) they work with are extremely low - just 2.0 kW for the average non-electrically-heated house (per 1.2.4.1 of the document) - and not really a ‘maximum’ in the normal sense; rather they are ‘peak expected averages’, averaged over both time and consumers. Such ‘averaging’ would be expected to work reasonably well for most of the time, but one would equally expect that there would occasionally be times when the total instantaneous demand (hence VD) rose to considerably more than those ADMD figures - such is the nature of statistics! For example, the 24 kW total ‘ADMD’ of 12 connected properties could well be exceeded, for at least a short time, if one or two of those consumers switched on 10.5 kW showers at roughly the same time. It would still probably average out at 2 kW/property over a ‘reasonable period of time’, but for 5 or 15 minutes, the demand (hence VD) could be something like double that average - and it’s that sort of voltage fluctuation that I personally have not noticed.
It is also interesting to read in 5.4.1 of the document that they work to a recommendation that the ‘step voltage change’ in response to switching on a single-phase load of 7.2 kW should not exceed 3%. Although they describe 7.2kW as “i.e. an electric shower”, this implies that they would presumably regard a voltage drop (in their
main) of about 4.4% (aka ~10.1V) when someone switched on a 10.5 kW shower as ‘acceptable’. Those are the sort of sudden drops in voltage that I’ve personally never observed or been aware of.
... but I’m still reading!
Kind Regards, John