The system will still meet G3 regulations as the boiler now forms the overheat protection.
The system will still meet G3 regulations as the boiler now forms the overheat protection.
That is extremely helpful, many thanks for taking the time.
I'm contemplating going full WC controls. I'd like to talk to people with the 400 series boiler to see how it benefits and if there's any reduction (or increase) in heating bills. I had a vaillant engineer out today, and he was raving about it (maybe he would!). He said he had it installed in his house. The vaillant cycling blog worries me as it's the high KW 400 series boiler which had problems with the WC controls.
I think, as you say, investing in the VR65 and rewire without the vaillant controls is probably a little pointless.
vr66 with the 47O is fine...with the mixing valve...
Bunny this is great information, but shoiudn't installers know all this before the public?
This may have been done elsewhere, but did you REALLY need 38Kw?? Pity about the standard S Plan you have - Sizing a boiler with a HW priority system (VR65) means you only need to size for the largest load, possibly the cylinder, at around 18-20Kw for a Megaflo.
The main problem with the 438 is the high output on minimum output (about 6.5Kw) and the start up output (about 26Kw) for 50 seconds REGARDLESS of the setting in D.0. This has been addressed in later release PCBs AFAIK, but is not helped by over zealous installers/customers thinking 'bigger is best'. The best and most efficient boiler is the correctly sized one!!!!
Lastly, don't think a 5M or even a 6M pump will do, it probably won't. Due to the need to shift 27 L/min through the boiler to extract 38Kw than a larger pump than a 'domestic' model is sometimes needed.
I have assumed: flow = 75°C; return = 55°C. (20°C differential)
The index rad is on the ground floor, but not the one suggested by the OP. It is the top right corner. The loss is 2.12m. The worst rad on the first floor is only 1.09m.
You won't listen fezster so what is the point?
The 15/60 that has been installed on the ground floor zone is 'robbing' (laymens terms so it is understood) any head/flow available from the 15/50 in order to circulate any water through the upstairs zone (when both calling for heat) , it has been said umpteen times the circulators must be installed in series BEFORE any zone valves , either remove the 15/60 and install it downstream of the 15/50 or simply remove both circulators and fit a 25/80......................or leave the circulators in situ and install an additional 15/60 to first floor zone.
I must admit, that with both zones open, the upstairs was taking a lot longer to heat up. *However* - since increasing to 30KW, both heat up in an acceptable time.
This whole saga comes down to a £500 quid circulator?
Combine its cost, electricity consumption and then it will help negate the benefits from a so called efficient boiler!
If it was mine I'd either be ripping the boiler out or the pipe work or both!