I had read that radial circuits were rare in the UK (although that info might be out of date), but I was aware that it was the norm in other countries.
|Prior to WWII, sockets circuits were all radial in the UK. After the war, the concept of ring circuits was introduced (allegedly because of a belief that it would reduce requirements for copper, at a time when limited amounts were available) and then became more-or-less the norm for new sockets circuits for a number of decades.
I don't know much about the pro's and con's of ring and radial, but since my first surprise a few years back I am aware that a ring is likely in UK homes.
I'm sure that they are still much more common than radials (for sockets circuits) but, as I said, that seems to be changing.
There really are very few 'pros' of the ring final circuit. Whether or not it requires 'less copper' depends on the physical location of the sockets - if they are arranged ('radially') in roughly a straight line radiating from the CU, then a ring final will require
more copper than the corresponding radial circuit. The main theoretical advantage is that it allows a cable rated at as low as 20A to be used in a 32A circuit but, in practice, that is not often a very significant advantage. If, as is commonly the case, 2.5mm² cable is installed by 'Method C' it has a CCC of 27A (and hence a 25A 2.5mm² radial is OK), which is not much less than 32A. About the only other 'pro' is that it provided 'CPC redundancy', which might be perceived as a safety advantage.
As for 'cons', if one has socket(s) close to one end of a ring, it is theoretically possible to overload the cable of the 'short' leg of the ring - and designers are meant to take steps to render this "unlikely for long periods". The fact that there is "L & N redundancy" is also really a 'con', since the ring can break, hence theoretically possibly overloading some of the cable, without the user being aware of any problem.
As EFLI has pointed out, rings are only used for sockets circuits, even in the UK, everything else (e.g. cookers, showers, immersions, virtually all lighting etc. etc.) are supplied by radial circuits.
I did, in the first sentence of of my first post.
Not really. You
said it was a ring circuit, but it was not until post #16 that you told us that you had previously measured the voltage on both cables disconnected from a socket on the same circuit
Without that information, your 'two cables' socket could have been on a radial circuit!
Kind Regards, John