do you mean the hob is on its own dedicated circuit? Not connected (incorrectly) to a socket circuit, or one that is also used for something else, such as a shower?
And you mean that the 32A hob breaker tripped? And nothing lost its power apart from the hob?
That is most irregular. A hob doesn't usually trip the breaker, and 32A should be plenty.
An electric hob never plugs into an ordinary socket (a gas hob can, because it uses very little electricity, just enough for the ignition spark).
An electric oven can be supplied from a 13Amp UK plug, provided it is a single oven (no secondary oven or separate grill compartment) and was designed for the UK market with a plug. Some continental, or catering, ovens may be intended for a 20A supply. Double ovens can't be plugged in.
It's not clear from your post if the oven is connected to the same circuit as the hob, or is on your general socket circuit.
However...
An electric hob ring takes maximum load when you first turn it on from cold. After it has reached your chosen temperature, it then clicks off and on, so it's unlikely that all 4 rings would take maximum power at the same time. Unless you turned them all full on, from cold, together. Is that when it tripped?