Any confirmation?
Unless I'm missing something new in later editions of the regs or other guidance that I hold:The OP has stated that there is no socket on the cooker switch therefore with 14.95kW of appliances there is still 5kW "to play with" for the usual diversity arrangement. Is this not enough to accommodate an induction hob even if it were different than a conventional hob?
Incidentally 14.95kW after diversity is 25.7A - not 29A as stated above.
Do you mean other than first hand experience?Any confirmation?
Use 240 as the manufacturer will have done - even less at 230V.Unless I'm missing something new in later editions of the regs or other guidance that I hold:
14950/230 = 65A
10+(55*0.3) = 10+(16.5) = 26.5
I mean the confirmation I asked for in the post to which you responded.Do you mean other than first hand experience?
My gut feeling would be to assess installation method of existing cable, if 6mm there is posisbly a good chance it could go on a 40A breaker, and thebn put a couple of 16A and one 32A breaker in an enclosure in one of the units near the ovens and if you are luckly with positioiung then the flexes to the appliances can come straight into it through stuffing glands with no messing around (Assume there is an isolator on the incomming supply - check thats suitably rated). If the supply had to remain at 32A then 95% you'd get away with it, but if you don't, it'll probably be at christmas or other inconvieninet time. Check the RCD as well, if its type AC then it really needs upgrading to A if introducing an induction hob.
Ah. The old gut feeling and Christmas reasoning.
Is there anything official to confirm your gut? If not, then ...
Not a silly one as it goes.
Any confirmation?
Do you mean other than first hand experience?
What have I missed?I mean the confirmation I asked for in the post to which you responded.
Oh I know all that and having been criticised within this forum for applying such calculations.Then you were taught incorrectly.
You are still using 230V on Wattages that will have been given for 240V.
Then don't bother replying, then.Oh I know all that and having been criticised within this forum for applying such calculations.
I have on a number of occasions worked with equipment with ratings plates calculated at 230V or even 220V.
Therefore I now revert to our standard voltage calculations and avoid making assumptions until I know the facts.
Without knowing the models being proposed and therefore the actual power ratings I have nothing else to go on.
Without knowing the models being proposed and therefore the actual power ratings I have nothing else to go on.
FFS we can all shout and holler.
Having been in the situation of a cooking appliance tripping the MCB on overcurrent during heavy use (as it happens not at Christmas) I don't think the original comment is as silly as many would seem to think.Ah. The old gut feeling and Christmas reasoning.
Is there anything official to confirm your gut? If not, then ...
although I'd put the figure way higher at above 99% with a number of 9's after the decimal point.95% you'd get away with it,
2 x Neff B64CS71GOBWhy don't you tell us what models of appliance you have in mind?
It would also be useful to see a pic of your consumer unit
And very very useful to know the size of your existing cable.
I previously had a range circuit with a 40A MCB.