I'm on holiday, and being a bit OCD I can never resist looking at the electrics (and other things) in the places we stay. I tend to send the host an email afterwards with any constructive comments I can give them.
The CU is an old 8-way Wylex board retrofitted with plug-in MCBs. There's also an RCD (30mA) between meter and board. Supply looks lke TN-C-S via overhead wires, but I also see an earth rod round the back. Labels suggest last inspection was in 1998.
I'm thinking the single RCD would be code C3 as it doesn't divide the installation at all so one fault would take out the whole cottage - but it's not, in itself, dangerous.
How would you code the CU ? Is it no code as there's nothing really wrong with it ? Or C2 as anyone can pull an MCB without any tools and leave a live hole that things could be poked into ? Or C3 because it's not really that serious and there's an RCD upstream of it ? I'm leaning towards C3 as live parts are less accessible than in most light fittings.
The CU is an old 8-way Wylex board retrofitted with plug-in MCBs. There's also an RCD (30mA) between meter and board. Supply looks lke TN-C-S via overhead wires, but I also see an earth rod round the back. Labels suggest last inspection was in 1998.
I'm thinking the single RCD would be code C3 as it doesn't divide the installation at all so one fault would take out the whole cottage - but it's not, in itself, dangerous.
How would you code the CU ? Is it no code as there's nothing really wrong with it ? Or C2 as anyone can pull an MCB without any tools and leave a live hole that things could be poked into ? Or C3 because it's not really that serious and there's an RCD upstream of it ? I'm leaning towards C3 as live parts are less accessible than in most light fittings.