I like the idea of improving safety, however when some one is found in difficultly as sea, the RLNI will send out a lifeboat with a crew to save them, even when they are risking their own lives to do so. This is repeated with many of the fire and rescue services. So the idea of risk assessment does not really pan out with these events, there will always be some risk with everything we do, and care is required so when trying to reduce the risk, the reverse is not the case.
This happened with the socket protector,
to my mind unless marked BS 1363 it should not be put in a 13A socket, and to date not found one marked BS 1363, I had this argument with a woman from the council who was insisting that before the house was used for child care these silly items were put in every socket a child could reach, the person who marketed these should get an award for selling so many useless bits of plastic.
However in the EU where shuttered sockets were not the norm, there equivalent likely made sense. OK this is an extreme case, but we have many cases where well meaning people in authority have issued the wrong advice. My mother was disabled and also had alzheimer's so the council fitted a new kitchen and sent some one to tell my mother how to use the new equipment, the woman dully arrived and told my mother to switch off the oven at the FCU when finished, this resulted in the carcase overheating, and the clock stopping, and the oven failing to work again until the clock had been reset, and my mother would not take my word not to turn it off at the FCU I had to get the woman back to tell her. So on inquiry it seems she only had a gas oven, on asking if she turned off the gas tap each time she finished with it, the answer was no, so why do it with electric?
All best intentions, but not enough thought had been used.
As stated each issue of BS7671 gives the date at which new designs need to take it into account, so if the installation has not degraded and it passed when installed, it should still pass.
However that does not really work where the requirements have been clarified rather than changed.
BS7671:2001 said:
314 INSTALLATION CIRCUIT ARRANGEMENT
314-01-01 Every installation shall be divided into circuits as necessary to:
(i) avoid danger and minimize inconvenience in the event of a fault, and
(ii) facilitate safe operation, inspection, testing and maintenance.
314-01-02 A separate circuit shall be provided for each part of the installation which needs to be separately controlled for compliance with the Regulations or otherwise to prevent danger, so that such circuits remain energised in the event of failure of any other circuit of the installation, and due account shall be taken of the consequences of the operation of any single protective device.
314-01-03 The number of final circuits required, and the number of points supplied by any final circuit, shall be such as to facilitate compliance with the requirements of Chapter 43 for overcurrent protection, Chapter 46 for isolation and switching and Chapter 52 as regards current-carrying capacities of conductors.
314-01-04 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energising of a final circuit intended to be isolated.
BS 7671:2008 said:
314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation
(v) mitigate the effects of electromagnetic interferences (EMI)
(vi) prevent the indirect energizing of a circuit intended to be isolated.
314.2 Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
314.3 The number of final circuits required. and the number of points supplied by any final circuit, shall be such as to facilitate compliance with the requirements of Chapter 43 for overcurrent protection, Section 537 for isolation and switching and Chapter 52 as regards current-carrying capacities of conductors.
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.
The "(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation" makes it clear RCD's are considered as forming circuits, and in real terms we should consider ⅓ of the RCD rating as a safe level, so we should check that the back ground leakage does not exceed 9 mA, however I will admit I have never tested, mainly as my clamp-on does not read that low, with the old 100 mA we were looking at 33 mA or less, but my meter would not measure that either. So some one could go to an installation I had installed and say it does not comply, it needs more than 2 RCD's. However what we are really looking at is test methods, and in hind sight, and hind sight is easy, I got it wrong, the ½ rating tests should be done with all MCB's turned on. If it does not trip with MCB's on the 15 mA plus leakage is not over 30 mA, but 30 mA test should be done both MCB's off and on, to ensure no DC component will stop the RCD tripping, but oddly we are not required to do this, or even check what type of RCD is fitted. May be just as well as my old installations may fail.
So if an installation fails, OK word is unsatisfactory, and nothing has degraded, can you call back the guy who installed it and demand it is corrected FOC? or if over 10 years old, the last guy who did a PIR (now called EICR) and passed it? If some thing has degraded, or been altered by unknown persons (Owner) then OK it may fail now but not when last checked, but no RCD sprouts wings and flies off.
But the oldest copy of BS 7671 I have is 2001, before that date I used the firms copy, so OK I know 1966 the rules on earths for lights changed, but I remember having to earth window frames at one point, what year that started and stopped I don't know, but if this was 1981 to 1991 (15th Edition) should I fail a property if built in this period and there are no bonding wires to window frames? The same applies distance of a socket to a sink, I seem to remember it was in one of the early editions.