A few random comments to the above ...
Yes, there are many different arrangements that are labelled "UPS" :
At the smaller end they are pretty well all "standby" systems where an inverter is started up and the load is transferred to it by a transfer switch. Some will keep the inverter running (on no load) and synchronised to the mains so as to allow faster switchover, but most don't.
Having an AC-DC converter, DC bus, and DC-AC inverter is generally called double conversion and gives much better isolation from mains "sh*t" like spikes etc - as well as zero transfer time since the load is never not already running from the inverter. The main reasons for not using double conversion are :
- You need full load, unlimited time, rated converters - whereas a standby system only need an inverter rated for as long as the batteries last, and the battery charger can be much lower rated.
- You are doing two conversion which both involve losses - so you are permanently losing a few % of your supply in heating up the room.
Also, for some of the double conversion units I've worked with, surprisingly the DC bus is not directly coupled to the batteries - there's a DC-DC converter between battery and DC bus, and a separate charger. So the DC bus is fed by two converters (one from AC, one from battery), and the AC-DC converter can't charge the batteries - guess it made sense to whoever designed it !.
And in general, the higher the power, the higher the battery voltage - our 16KVA system at work uses nominal 120V (so 136V float) batteries.
And there is quite a bit of IT kit which can (either by selecting a DC variant, or adding additional module(s)) run off DC - usually 48V for commonality with telecoms supplies.
I have to admit, I have a couple of times wondered about the possible short circuit current available from the batteries on our system - 120V, cabinet full of low-impedance AGM batteries. Each string has a 60A HRC fuse, I forget what rating the main cabinet fuse is.