Completely over the top. 1.0mm cable is the norm for lights on a 6 amp breaker even if it is buried in loft insulation.
How many metres before voltage drop becomes excessive and 1.5mm² is necessary.
Required Cable Size for 1.4 kW of lighting 30 metres from CU
Cable Size 1.5 mm
Voltage Drop 5.30 Volts.
Percentage Drop 2.3%
Current Load 6.09 Amps
Max Cable Load 14.5 Amps
Note that the cable is rated as being able to safely carry 14.5 Amps but if carrying 6 amps then the voltage drop is too high to meet the regulations.