Indeed, but where I imagine your certificate would run into difficulties is if the Zs was greater than 0.8U0/Ia, but still 'OK' - since your certificate would then think/indicate that it was 'not OK' ... as EFLI reminded me yesterday, Appendix 14 says that if Zs is greater than 0.8U0/Ia, one may undertake a more detailed calculation taking temperatures into account - and that calculation could indicate that the Zs was actually acceptable.On our certificate where it states "Maximum Zs permitted" it looks like they use a de-rated value, as they list 6.13 ohm for the lighting circuits, which equates to 230/30 x 0.8. So I think what they're doing is noting the max permissible Zs at ambient temperature so it can be directly compared with actual measured R1+R2 and Zs.
That would make mathematical sense, although I don't recall having seen it stated as such. As for the magnitude of the load, the OSG is obviously a bit behind the times, since, IIRC, it wants one to consider each lampholder as representing a 100W load.Regarding voltage drop, is it not the convention that lighting circuits are assessed as if the total distributed load was a single point load at 50% of the length? I can't remember where I heard that, so may not be up to date.
Kind Regards, John