Currently have an electric double oven and gas hob. The oven is on a dedicated 32A radial circuit from the CU. Wired with 6mm T+E cable running in a bundle through free-air in the ceiling cavity for approx 10 meters, then clipped to thermalite block behind plasterboard for the last 2 meters to the oven isolator.
The prospective new appliances have ratings of 3.6kW for each oven and 3kW for the induction hob, for a total of 10.2kW or ~42.5 Amps. Under the diversity calcs listed here: http://wiki.diyfaq.org.uk/index.php?title=Diversity typically this would equate to:
10A
+ 30% of the remainder = 0.3*(42.5-10) = 9.75A
+ 5A for the socket on the cooker isolator
= 24.75A
Which falls inside the 32A circuit limit, with a fair amount of headroom. However - I know the socket on the oven isolator will not be used as it's about to be boarded up behind some new kitchen units, so for this specific installation there will be another 5A of headroom. Realistically, my typical peak usage might be the 2 ovens on simultaneously with 2 out of the 4 hobs, which would come in at approximately 36 Amps if everything happened to be using max current all at the same time (unlikely).
Given above diversity calculations, it would seem to be acceptable to wire the induction hob into the existing 32A radial by spurring from the existing oven isolator to a new isolator for the hob using 6mm cable? The additional run would be approx 6 meters clipped to thermalite behind plasterboard.
Would you agree?
10A
= 24.75A
Would you agree?