It doesn't work like that for cooking appliances.

Because of 'diversity' a 32A cooker circuit can supply upto 20kW of cooking appliances.
Thought it was 15kw? Asking for a friend....lol.

20kw works out to 33 amps.
You might get away with 19kw.
 
Sponsored Links
IMG_20241102_110636_HDR.jpg



IMG_20200111_143557.jpg


All in the current and previous editions of the On Site Guide.
Previously in the Regulations for the Electrical Equipment Of Buildings starting with the 10th edition published in 1934 and contained in every edition since then until the information was moved in the OSG.

1934.png


The only difference is that is was 10A + 50% long ago, revised due to cookers becoming more efficient as insulation was added to ovens.
It should be revised again as induction hobs are significantly more efficient than those with resistive elements.

Anyone calling themselves an 'electrician' or anyone who owns any edition of these publications from the last 90 years should be aware of this information.
 