Nope, wrong again. 6mm² T&E is 47A.Your right on the boarder line at 41.66 amps. 6mm is rated at 41amps.
Nope, wrong again. 6mm² T&E is 47A.Your right on the boarder line at 41.66 amps. 6mm is rated at 41amps.
Thought it was 15kw? Asking for a friend....lol.It doesn't work like that for cooking appliances.
Because of 'diversity' a 32A cooker circuit can supply upto 20kW of cooking appliances.
Some might say you can take into consideration "Maximum diversity factor" that not everything will be on at the same time. It will be at Christmas.
Nope, wrong again. 6mm² T&E is 47A.
Not if run in a wall "like the post is saying" it has a lot less of an amperage rating as any heat cant be disbursed so easily like an open clipped cable that can be classed for a 47 amp rating.Nope, wrong again. 6mm² T&E is 47A.
Reference method C clipped direct as in buried in the wall=47A.Not if run in a wall "like the post is saying" it has a lot less of an amperage rating as any heat cant be disbursed so easily like an open clipped cable that can be classed for a 47 amp rating.
6mm² T&E has a maximum CCC of 47A.
6mm² T&E has a maximum CCC of 47A.
FFS. Then don't install it under a foot of insulation.not under a foot of insulation it doesn't
20,000W / 240V = 83.333A -10 = 73.333A x 0.3 = 22A + 10 = 32A20kw works out to 33 amps.
You might get away with 19kw.