Hi,
Just got a new Worcester 27CDi fitted replacing an ageing thermal store and small ideal boiler.
The boiler seems very nice, DHW seems fine, boiler rund perfectly for that. I am slightly confused by the CH side of things.
The rads are all heating nicely, and my existing TRVs are kicking in as I would expect. Two rads have no TRVS so run constantly depending on what my wall thermostat is set to.
For purpose of testing I set it to 30c just to keep it running although the living room prolly got to about 23c-24c
I am not sure if my boiler is cycling properly or not though. Plumber will said he will come take a look if I am not happy but not sure I am wasting his time.
With the boiler on max the CH demand the boiler kicks into life and starts supplying the rads, the display on the boiler goes up to around 85-88 and then the burner switches off, boiler continues running and the temp of the return will gradually drop to 40 sth and then the cycle repeats. If I set the boiler to lower than max I get the same cycle but it will top out at 60-80 odd depending where the dial is.
Reading the manual for the CDi is a about as much use as a chocolate fire guard, with phrases such as "anti-cycling, burner modulation" etc.
From a supplier website I got this:
'Central heating mode
On a Central Heating demand, the boiler will initially fire at minimum output before modulating upwards to meet the actual system requirement. Electronics within the boiler continually monitor the heating flow temperature increasing or decreasing output on demand. An anti-cycling device makes the Greenstar CDi range particularly suitable for use on systems with TRV's (Thermostatic Radiator Valves).'
That to me suggests the burner should always be running and not ramp up the temp to 88 and then turn the burner off, it should keep the burner running and keep the temp from going over 88, ie to modulate and anti-cycle. Am I just understanding it wrong and should the boiler run and just switch the burner in and out?
Is my boiler working properly or is it doing something naughty?
Cheers,
Just got a new Worcester 27CDi fitted replacing an ageing thermal store and small ideal boiler.
The boiler seems very nice, DHW seems fine, boiler rund perfectly for that. I am slightly confused by the CH side of things.
The rads are all heating nicely, and my existing TRVs are kicking in as I would expect. Two rads have no TRVS so run constantly depending on what my wall thermostat is set to.
For purpose of testing I set it to 30c just to keep it running although the living room prolly got to about 23c-24c
I am not sure if my boiler is cycling properly or not though. Plumber will said he will come take a look if I am not happy but not sure I am wasting his time.
With the boiler on max the CH demand the boiler kicks into life and starts supplying the rads, the display on the boiler goes up to around 85-88 and then the burner switches off, boiler continues running and the temp of the return will gradually drop to 40 sth and then the cycle repeats. If I set the boiler to lower than max I get the same cycle but it will top out at 60-80 odd depending where the dial is.
Reading the manual for the CDi is a about as much use as a chocolate fire guard, with phrases such as "anti-cycling, burner modulation" etc.
From a supplier website I got this:
'Central heating mode
On a Central Heating demand, the boiler will initially fire at minimum output before modulating upwards to meet the actual system requirement. Electronics within the boiler continually monitor the heating flow temperature increasing or decreasing output on demand. An anti-cycling device makes the Greenstar CDi range particularly suitable for use on systems with TRV's (Thermostatic Radiator Valves).'
That to me suggests the burner should always be running and not ramp up the temp to 88 and then turn the burner off, it should keep the burner running and keep the temp from going over 88, ie to modulate and anti-cycle. Am I just understanding it wrong and should the boiler run and just switch the burner in and out?
Is my boiler working properly or is it doing something naughty?