Worchester 30I Pressure keeps creeping up

Thank you for your advise, as far as I'm aware there's only one loop which the key has been kept out of for the full night. I have had no leaks from it.

The preassure raises without the CH turned on. It raises very very slowly. Like 0.3 an hour.
 
Sponsored Links
OK - isolate the cold water into the boiler - if it stops and everything else is equal re filling loops etc then it has to be the plate.

Has the system been really dirty? Plates only tend to pinhole or block up when corrosion is bad or some other chemical has damaged it.
 
It doesn't look dirty, a month ago the plate was leaking because the rubber rings where pretty much melted and I change all 4 rubber rings.
 
Sponsored Links
Yes you was the first to say this and you was 100% correct. Thanks you amazing person!
 
I got told by the guy who installed my parts they all good. Thanks for your concern but it seems you are being a little aggressive. Maybe you did not understand my messages but others did. Have a good night sir.
 