Another simple - just change a light switch job.
Customer reports a big flash, tripping and lights not working.
I arrived to find an obvious brand new 2G switch with a big black flash mark and didn't move properly. Customer insists it has not been touched despite some debris below on the otherwise clean carpet.
I found 5 cables, only No5 having an earth wired with cables 4&5 going off to a couple of 1G switches thus:
I noted the connexions and numbered cables as above then removed the faulty 2G switch
Cable 1 = 40Ω r-bk, 2Ω bk-earth, 43Ω r-earth. (Main switch in fuse board removes earth readings)
Cable 2 = 120Ω r-bk
Cable 3 = 41Ω r-bk, 76Ω y-bk, 139Ω r-y
Cable 4 and switch buzzed out perfectly
Cable 5 and switch buzzed out ok except grey was open circuit and switch didn't move properly.
The 2 associated ceiling roses looked like they are from the 60's with untold layers of paint, as is much of the installation.
And to crown it all there was a power cut.
I have fixed this and sent a report to the managing agent pointing out the importance of regular reports and the need for updating what's installed.
Ideas anyone?
Customer reports a big flash, tripping and lights not working.
I arrived to find an obvious brand new 2G switch with a big black flash mark and didn't move properly. Customer insists it has not been touched despite some debris below on the otherwise clean carpet.
I found 5 cables, only No5 having an earth wired with cables 4&5 going off to a couple of 1G switches thus:
I noted the connexions and numbered cables as above then removed the faulty 2G switch
Cable 1 = 40Ω r-bk, 2Ω bk-earth, 43Ω r-earth. (Main switch in fuse board removes earth readings)
Cable 2 = 120Ω r-bk
Cable 3 = 41Ω r-bk, 76Ω y-bk, 139Ω r-y
Cable 4 and switch buzzed out perfectly
Cable 5 and switch buzzed out ok except grey was open circuit and switch didn't move properly.
The 2 associated ceiling roses looked like they are from the 60's with untold layers of paint, as is much of the installation.
And to crown it all there was a power cut.
I have fixed this and sent a report to the managing agent pointing out the importance of regular reports and the need for updating what's installed.
Ideas anyone?