Thanks. That much I understood, but I was surprised by the implication that the core could become saturated with a current something between 15mA and 100 mAIt affected by the magnetic core - higher current increases the magnetic field in the core and as it approaches magnetic saturation the impedance decreases.
An inductor with a magnetically saturated core isn't an inductor any more.
In any event, the figures they presented would seem to indicate that, in the absence of any additional residual current due to connected equipment, the meter they were talking about would always give a reading which was about 0.5 Ω too high. Is that what they are saying/implying?
Indeed, but if I understand correctly, the OP undertook his testing, with varying Zs results, when there were "no loads on the circuit".If nothing else is connected to the installation then the additional impedance should be consistent, however in real installations there is likely to be some residual current from connected equipment, and as that varies the additional impedance seen by the test equipment will also vary.