2 Pole Tester Usage

Touch the probes together.

Does it beep and show a different reading than Voltage?

When I touch the probes together, everything lights up and the unit beeps. This includes the voltage display and the red lights across the side indicating the voltage detected. I was advised to rely on the lit up voltage display as opposed to the screen display.

upload_2021-4-26_12-20-29.png
 
Sponsored Links
What does the display show when you touch the probes together?

upload_2021-4-26_12-28-8.png


Switch off power for continuity tests on circuits.
 
Are you getting voltage readings? If so what are they? Or is it continuity as per efli?
 
Sponsored Links
What does the display show when you touch the probes together?
A correction to what I stated earlier: if I briefly touch the probes together I get a beep and the following (circled in red) lights up:
upload_2021-4-26_12-53-24.png


If I leave the probes in contact for around 5 seconds, everything lights up and beeps. I get a reading of 1.8888.
 
Switch off power for continuity tests on circuits.
Double pole switches - Main Switch, RCCB, RCBO etc will separate the N and E.
RCBOs are usually single-pole, aren't they?

However, your suggestion was ...
You could test between N and E on low ohms range. There should be continuity of an ohm or so.
... and I'm finding that hard to understand. With the N 'isolated' (by a DP switch), one would (in the absence of an N-E fault) surely not see 'continuity' (low resistance) between the N and anything, would one?

Or am I missing something?

Kind Regards, John
 
RCBOs are usually single-pole, aren't they?
Some aren't, but yes.
I should have added another qualifier but can't explain everything.

However, your suggestion was ...
... and I'm finding that hard to understand. With the N 'isolated' (by a DP switch), one would (in the absence of an N-E fault) surely not see 'continuity' (low resistance) between the N and anything, would one?
Yes, but I added
"Double pole switches - Main Switch, RCCB, RCBO etc will separate the N and E."
intending to mean don't do that.

Or am I missing something?
Just switch off the MCB or pull the fuse.


Sometimes it is difficult to explain everything about the obvious.
 
Yes, but I added "Double pole switches - Main Switch, RCCB, RCBO etc will separate the N and E." intending to mean don't do that.
Ah - I took it to mean "do do that" - my apologies :)
Just switch off the MCB or pull the fuse.
That's fair enough with TN-C-S.

However, with TN-S it's very likely that there would be at least a very small (AC) potential difference between N and E, which presumably would/could completely mess up (in an unpredictable fashion) attempts to measure resistance with a meter - and with TT it wouldn't surprise me if a resistance meter (using very low voltage DC) failed to find much in the way of continuity at all (and certainly not the "ohm or so" you suggested).

We don't know what earthing system the OP says, but it sounds as if the measurement would only be helpful if it were TN-C-S (and that no DP devices had been 'switched off').

Kind Regards, John
 
The danger is always in assumptions- (the other danger lurks when you believe what people say they have done or what has happened without any knowledge of their level of competence or experience).
Thus it is unwise to assume that just because you can see an earth in a backbox it will always be correctly connected at the other end of the cable.
The much maligned voltsticks and neon testers must not be relied on to prove dead but can be handy for first line fault finding (if a known good light isn't working but voltstick lights up its good odds you have a neutral fault).
 
The much maligned voltsticks and neon testers must not be relied on to prove dead but can be handy for first line fault finding (if a known good light isn't working but voltstick lights up its good odds you have a neutral fault).
Very true, and I suspect that many/most of those who do the maligning (certainly including myself) actually do use them (for appropriate purposes) more than they would probably want to admit! However, that requires a user who fully understands the potential limitations, hence 'risks' - and that probably is not the case for anyone who 'needs to ask questions'.

Safety-wise, there isn't really an issue if the neon does light up - the only 'risk' then is that one is being mislead by some 'stray pick up'. The true dangers all arise when it does not light, and no-one who 'understands' would read very much into that.

Kind Regards, John
 
I always use my red probe on live and black on N/E as part of the two tests. Additionally, I also test across N and E now, as per suggestion above.
In any of these tests, does it matter which coloured probe I use on which terminal?
 
I always use my red probe on live and black on N/E as part of the two tests. Additionally, I also test across N and E now, as per suggestion above. In any of these tests, does it matter which coloured probe I use on which terminal?
No - with AC it makes no difference.

However, it's probably best that you stick to the convention you mention since it might serve to remind your brain that when measuring DC voltages it does matter (red=positive and black=negative, assuming they are plugged into the correct sockets!).

Kind Regards, John
 
With a modern digital meter it does not even matter with D.C. If you do it the other way round it just indicates -ve volts.
 
With a modern digital meter it does not even matter with D.C. If you do it the other way round it just indicates -ve volts.
aha...I think that's what my Fluke T130 does. If I see -ve volts with DC, I will use that as a prompt to reverse the probes.
 