Please don't shout.But you do not KNOW that it is the opinion held by every single maker of 13A sockets in the world.
Correct, I do not know that. In fact I suspect that there are some cheats and shysters among the manufacturers of 13A sockets in some parts of the world who find it convenient to make a product that only passes the specified tests of the standard.
Correct, I don't. BS1363 does not define "excessive temperatures", and it does not define "normal use". Instead it uses a carefully-designed test to verify that the requirement to not attain excessive temperatures in normal use is met. This test contains some parameters that cannot be considered "normal use"; the twin socket-outlet is flush-mounted in a wooden block, has only a single cable connected, one of the sockets is loaded at 14A, the plugs contain heaters, the earth pins of the plugs are not connected. (Yes, I know that there will only be a single cable if the socket-outlet is at the end of a radial or spur, and I know that not every appliance that will be connected via a 13A plug requires an earth connection.) The maximum allowable temperature rise is specified.You do not KNOW that 13A through each outlet for any amount of time is what is considered normal use in the context of BS 1363.
I know that there is not a test relating to the ability of a socket-outlet to carry 13A for several hours. I am aware of the requirement that a socket-outlet shall not attain excessive temperatures in normal use.And not one of them is a requirement which relates to the heating effect of a load sustained for several hours.
Not one.
And you know that.
The standard does not say that they must be capable of carrying 13A in each outlet concurrently, because it does say that 13A socket-outlets shall be capable of carrying (and making and braking, and switching, where relevant), and it does not relax those requirements for twin socket-outlets.No, I think they need not be because the standard does not say that they must be. And because what it does say, in this context, is that they must not overheat in normal use (a condition not defined), and that if they don't overheat at 14A+6A for 4-8 hours that is considered proof that they won't overheat in normal use.
If the criteria for passing that test included only a measurement of the average temperature, you'd be right. As I tried to explain, the test was apparently designed to reveal hot spots, by overloading one of the outlets. It was considered by the members of PEL/23, including experts in the design. manufacture, and testing, that this test is sufficient, given the fairly benign temperature rises involved, to verify that the requirement that the socket-outlet shall not overheat in normal use, is met.Unless you are totally ignorant of what happens when a current flows through which has electrical resistance, you will know that the heating effect of 13A+13A will be greater than that of 14A+6A.
Therefore you know that at 13A+13A a socket which meets the requirement to not overheat at 14A+6A might not meet that requirement when the load is increased by 30%.
What I observe does not matter. The fact is that there are requirements relating to the ability of a 13A socket-outlet to carry 13A, and they are nor reduced for a twin socket.And it really doesn't matter how often, or how correctly, you observe that if it's OK at 20A it will probably be OK at 26A, at the end of the day you just do not KNOW.
I assume that the customer who had bought that non-conformant product would have a complaint to Trading Standards. They in turn would probably ask the opinion of a test house. TS would have the authority to demand the cessation of sale of those products and the destruction of stock.And if it managed to sustain that load for several hours I think most reasonable people would say that normal use probably doesn't involve running it flat out for several hours and that therefore it probably does comply.
But what happens between those two bounds? You said it yourself, it is undefined. If, after a period of time, which could be longer or shorter than an undefined period of time, the socket does overheat, what then?
Who would hold the manufacturer to account for the "unacceptable", or "non-compliant" behaviour of his product in that it failed to meet an undefined requirement?
And how would they do that?
That is of course correct. Similarly, nobody can know a duration for which a twin socket-outlet to BS1363 cannot handle 13A+13A.Unless and until somebody nails their opinion to the mast and goes to court and successfully argues that "normal use" means 13A through both sides for x minutes/hours/days/whatever, so that the "some undefined period of time" becomes defined through the precedent of the decision of a court, nobody can KNOW how long a socket claimed to be compliant with BS 1363 can handle a 26A load.
No. However there is an association to which these test houses belong, and they share information and interpretations of the grey areas in standards, so I have no doubt that that opinion is shared among the reputable test houses. There will always be manufacturers who will fail to comply with requirements of a standard.You and they have an opinion of how a twin socket should perform.
Do you or they KNOW that that opinion is shared, has always been shared, and will always be shared by every single manufacturer on the planet?
No they don't, but they will refuse to certify that the product conforms to the standard. They will also share the result of their tests with other test houses so that the manufacturer of the non-conforming product cannot simply shop around until he finds one that agrees with him.But if a socket fails to perform how they think it should, do they refuse to run the tests as specified in BS 1363 and refuse to certify that the socket passes the tests specified in the standard?
No, I don't, unfortunately there are cowboys among the test houses, just as there are among manufacturers.Even if they do, do you and they KNOW that every other testing house on the planet does the same?
No, I'm not discounting anything. I am repeating what I have been told. The test is not intended to simulate 'normal use', but it is to verify a requirement. The experts involved judged that, if a twin socket-outlet did not exceed certain specified temperatures after carrying 14A+6A for between 4 - 8 hours under the specified conditions, it would not attain excessive temperatures in normal use.So you are simply discounting the possibility that the defined period was chosen because "normal use" was not considered to mean a substantial load sustained for more than 8 hours?
No, whatever gives you that impression?You are simply discounting the possibility that if between hours 4 and 8 a socket has pretty much stopped getting hotter it can be considered to not be likely to get any hotter from 8 hours onwards?
And one lasts for 7 days, but in those cases the product is simply left in a test chamber for that period, with no need for any human involvement.Maybe so, but if so then they will be test houses which are unable to offer the full range of tests specified in BS 1363, because some of them last more than 8 hours. At least one lasts for 48 hours.
Exactly my point. A single cable is specified in order to limit the heat loss from the item under test, so as to shorten the time needed to achieve thermal stabilty. For the same reason, the plugs include heaters, and the earth conductors of the plugs are not connected.Let's not forget that BS 1363 actually specifies only one cable. If a second cable were to be connected then they would not be testing in accordance with the standard.
And yours was?But then the opinion you hold was not arrived at by reasoning in the first place.