We were always taught boiler then the Vent/Feed & pump with the horizontal (of the 'H' of the F&V) a max of 150mm between each other if not using an air separator. If that wasn't possible then the pump should be after the F&V as close as possible to it avoiding it being more than half way around the system & before the boiler. Single pipe systems are also notoriously sensitive to component placement.
If using a combined F&V in a domestic setup then we were always told to use the vent which was normally the same size as the main system pipe size, invariably 22mm.