Which should also be true of a TT installation.
Well, it would be true of a TT installation IF a TT installation had a "TN-C-C PEN" which could fail (which is what you were talking about, and I was responding to) - which it obviously doesn't!
But leads me on to something I've been thinking about at church. There's a metal oil pipe comes into the boiler room which I don't think is bonded. It's going to be earthed anyway as there's metallic elements all the way to the burner which is earthed. I'm thinking it should be bonded. But, outside it connects to a big metal tank sat on lumps of wood - and I'm wondering about loss of PEN conductor, particularly as it's overhead singles in the overhead supply. Do the nice damp blocks of wood make a good earth, or does the tank become live
We've discussed this, and variants thereof, before.
Whether or not, per regs, such a pipe requires main bonding depends on one's view as to whether it constitutes an extraneous-c-p. ELFI would (if one could disconnecting the pipe from 'incidental earthing) probably advise finding out by measuring the resistance from the pipe to MET. However, he would probably make that measurement when the wood blocks were dry (and conclude that it was not an extraneous-c-p, and therefore didn't need bonding) - at which point I would ask him how he knew that it would not know whether is would still be "no an extraneous-c-p" when the wood blocks were soaking wet!
In practice, I suspect that even 'soaking wet' blocks of wood would probably not provide a low enough impedance to earth to be able to result in a 'serious' electric shock (if pipe were touched simultaneously with something live), particularly if the wood blocks were not sitting directly oi bare earth - but I obviously cannot be sure of that.
If, by whatever process, one decides that bonding of the pipe
is necessary, then, in a TN-C-S installation, one has the same potential hazard as with an outside tap - and the only real solution to that is to put an 'insulating section' into the pipe where it enters the building.
In fact, since (as in your case) the pipe will very often be 'incidentally earthed', the hazard with TN-C-S (in the event of a PEN failure) exists even if one does
not bond it - so, again, if one is concerned about the very small risk, one should electrically isolate the outside pipe from the building's earthing system.
Kind Regards, John