Another BS 5733 "not quite"?

And if, as seems might be the case, BS 5733 affords a degree of flexibility in assembling a complete MF "accessory" (The coffin-shaped Wagoboxes are not made by Wago, nor are the Wagobox XL or XLA, and those are not made by the manufacturer of the first), why should someone not use MF connectors (e.g. Ideal), in an enclosure of their own choice and deem it an MF accessory?
[ I'm not sure that your bit in parenthesis is all that relevant since, although the manufacturers differ, the use of the name "Wagobox" presumably implies a close collaboration between Wago and the box manufacturers.]

We do not yet know whether BS 5733 includes any requirements in relation to the enclosure, other than (according to mfarrow) that it should include cable restraint. To do as you suggest would at least require knowledge that the "enclosure of one's choice" was compliant with any requirements in BS 5733 as regards the enclosure.

We do not yet know details of how what BS 7533 brings about the degree of down-rating and imposition of a maximum aggregate current for Wagos in a Wagobox. Are these generic requirements for any 'MF' connectors or are they perhaps Wago-specific? If you wanted to use connectors other than Wagos, you would need to know the answer, and what (if different) would be the corresponding requirements in relation to whatever connectors you had chosen.

Do we know that Ideal connectors, or other 'alternatives to Wago connectors' conform with the requirements of BS 5733 for MF connections? To do as your suggest would obviously require that they did.

The 'enclosure of your choice' would presumably not bear an MF symbol, and it appears that BS 5733 probably does not require it. However, if you wanted to be BS7671-compliant, there would have to be such a symbol. Are you suggesting that one should do as EFLI suggests and 'add that marking' oneself? (BS 7671 appears to be silent as to who may do the marking).

Kind Regards, John
 
Sponsored Links
[ I'm not sure that your bit in parenthesis is all that relevant since, although the manufacturers differ, the use of the name "Wagobox" presumably implies a close collaboration between Wago and the box manufacturers.]
It is relevant, as it's a scenario where Manufacturer A declares his product when used with ones from Manufacturer B to be compliant with a BS. It's not as if A is buying in parts from B and reselling them, or vice versa - the end user can buy the parts separately, at different times and from different sellers, possibly neither set of parts from either of the makers.

We have no idea how close the collaboration is between Wago and Connexbox, or Wago and Spelsberg (who make another box which takes Wago connectors), nor how close it needs to be. (Note - above I was confusing the Wagobox XL/XLA and the Abox sold by Wago - the former is made by Connexbox).

How close does the collaboration need to be between Wago (or Ideal) and anybody with a 3D printer? Or anybody selling boxes with a DIN rail and instructions on how to install Wago connectors and their rail mount holders?

This is what I mean about flexibility in assembling a complete MF "accessory".


We do not yet know whether BS 5733 includes any requirements in relation to the enclosure, other than (according to mfarrow) that it should include cable restraint. To do as you suggest would at least require knowledge that the "enclosure of one's choice" was compliant with any requirements in BS 5733 as regards the enclosure.
It would. Maybe a compression gland provides adequate restraint. Maybe a standard cable clip fixed to a pad in the box using a self-tapping screw would do. Maybe compliance with a BS EN 60670 standard for enclosures makes compliance with BS 5733 for the enclosure itself superfluous.

Remember this is what Wago say:

You need to bear in mind that BS 5733 isn’t a product standard. BS 5733 is more like a generic set of rules for products that aren’t covered by their own standard. The standard for Junction boxes is BS EN 60670 and the Wagobox with Wago 773 and 222 connectors is fully compliant with this standard up to and including the performance standard BS EN 60670-22.

That would mean that there are no rules for junction boxes in BS 5733 because they are covered by their own standard.


We do not yet know details of how what BS 7533 brings about the degree of down-rating and imposition of a maximum aggregate current for Wagos in a Wagobox. Are these generic requirements for any 'MF' connectors or are they perhaps Wago-specific? If you wanted to use connectors other than Wagos, you would need to know the answer, and what (if different) would be the corresponding requirements in relation to whatever connectors you had chosen.
upload_2017-11-29_23-42-5.png


This is an educated guess: the de-rating is based on conductor size, so using Ideal connectors with 2.5mm² conductors and derating them to 20A would be compliant.

Not a sound enough basis to go to market. But sound enough to claim reasonable skill and care, and best of knowledge and belief etc? Quite possibly.



Do we know that Ideal connectors, or other 'alternatives to Wago connectors' conform with the requirements of BS 5733 for MF connections? To do as your suggest would obviously require that they did.
I don't think we even know if any connector on its own can comply, or whether it has to be in an enclosure.


The 'enclosure of your choice' would presumably not bear an MF symbol, and it appears that BS 5733 probably does not require it. However, if you wanted to be BS7671-compliant, there would have to be such a symbol. Are you suggesting that one should do as EFLI suggests and 'add that marking' oneself? (BS 7671 appears to be silent as to who may do the marking).
If it's silent then adding it oneself cannot be invalid, prima facie.

Similar discussions here, and not the only place I've seen a suggestion of undue influence from Hager.

https://www.electriciansforums.co.uk/threads/maintence-free-jbs-mfjbs.113647/
 
.... Maybe a compression gland provides adequate restraint. Maybe a standard cable clip fixed to a pad in the box using a self-tapping screw would do. Maybe compliance with a BS EN 60670 standard for enclosures makes compliance with BS 5733 for the enclosure itself superfluous.
.....
This is an educated guess: the de-rating is based on conductor size, so using Ideal connectors with 2.5mm² conductors and derating them to 20A would be compliant.
.....
I don't think we even know if any connector on its own can comply, or whether it has to be in an enclosure.
"Maybe", "maybe", "maybe", "educated guess" and "we don't even know". .... As I've written countless times, we really can't discuss this matter sensibly unless/until we have a much clearer idea about what BS5733 actually says.

As for your final point above, if what we've been told is correct, it seems that BS 5733 does concern itself with the connectors themselves ....
....There's a list of tests for screwless terminals and separately "terminals for maintenance free accessories" which further include thermal cycling and 1512hr testing at rated current to check for volt drop.
If it's silent then adding it oneself cannot be invalid, prima facie.
I wonder whether you would say the same if we were talking about writing the information required by BS1363, "clearly and indelibly", on, say, a previously unmarked 13A fused plug? After all, the bits of BS 1363 and BS 1362 you posted appeared to be silent as to who was to do (or could do) the "marking".

Kind Regards, John
 
And now here is an interesting thing:

LINEFeaturesDiagram.jpg


So it is "BS 7671 compliant with ANY BS EN 60998 connector". Wago and Ideal connectors are BS EN 60998 compliant. But which bit of BS 7671 compliance are they referring to?

And what does "MF BS 5733 option" mean? That this is an option for MF BS 5733 compliance? Or that there are options for the product which are needed for it to be compliant?


I feel another closely worded clarification request coming on ;) It's academic really - this does not look like a low-cost product.

Interesting to note that cable ties are considered acceptable restraints - POP to use those in some way in a generic enclosure.
 
Sponsored Links
I wonder whether you would say the same if we were talking about writing the information required by BS1363, "clearly and indelibly", on, say, a previously unmarked 13A fused plug? After all, the bits of BS 1363 and BS 1362 you posted appeared to be silent as to who was to do (or could do) the "marking".
Quite honestly, John, I think it would be taking your quibbling-over-everything-with-a-claimed-devil's-advocate-justification far too far to suggest that it would not be the maker who is to do it.
 
Quite honestly, John, I think it would be taking your quibbling-over-everything-with-a-claimed-devil's-advocate-justification far too far to suggest that it would not be the maker who is to do it.
I totally agree - but it was you who, in response to my question, said that adding one's own 'MF' symbol to an unmarked enclosure to make it BS 7671-compliant would be 'valid' (which I took to mean 'acceptable')?

Kind Regards, John
 
That's a very different scenario if the standard for MF junction boxes does not require the MF symbol. All claimed compliance with BS 7671 is on the basis of best of knowledge and belief, exercise reasonable skill and care.
 
It's academic really - this does not look like a low-cost product.
Appearances can be deceptive, it seems.

http://lineproducts.co.uk/forumshop/index.php?main_page=product_info&cPath=2&products_id=25

In the end I never bothered to ask questions, but having found the online shopping part of their site I gleaned the following:

What turns it into a JB marked as MF is simply securing it shut with one of these instead of a normal cable tie:

MF%20Enclosure%20Ties.jpg


(a snip at £3.30 for 20), and following their instructions to use any of the connectors they supply (Wago or Ideal), derated to 20A.

The more I find out about the "requirements" for BS 5733 MF compliance the more of a farce it seems.

But it does look like a neat product, nice that they've got M20 threaded entries for glands. If you don't need it marked it looks as though it doesn't need a cable tie at all to close it.
 
The more I find out about the "requirements" for BS 5733 MF compliance the more of a farce it seems.
It is coming to look that way. However, as I keep saying, we really need a clearer idea of what these 'requirements' actually are.

Mind you, regardless of what BS 5733 says about the need, or otherwise, for marking, BS 7671 certainly does have such a requirement - and I'm not sure that having an 'MF' symbol on an attached cable tie would necessarily satisfy BS 7671's requirement for the JB to be 'marked'.
If you don't need it marked it looks as though it doesn't need a cable tie at all to close it.
It may not be applicable if (as presumably often/usually will be the case) it is not 'accessible' but, as I've said before, I think BS 7671 requires any enclosure which contains live parts to not be openable without the use of a tool. However, as I've said, I'm not sure whether this applies if it is not accessible. Do you know?

Kind Regards, John
 
It is coming to look that way. However, as I keep saying, we really need a clearer idea of what these 'requirements' actually are.
It is coming to look as if they are putting non-screwed connectors inside a box with cable restraints and the need for a tool to open it and an MF symbol somewhere.


Mind you, regardless of what BS 5733 says about the need, or otherwise, for marking, BS 7671 certainly does have such a requirement - and I'm not sure that having an 'MF' symbol on an attached cable tie would necessarily satisfy BS 7671's requirement for the JB to be 'marked'.
The people responsible for the LINE enclosure believe it does.


It may not be applicable if (as presumably often/usually will be the case) it is not 'accessible' but, as I've said before, I think BS 7671 requires any enclosure which contains live parts to not be openable without the use of a tool. However, as I've said, I'm not sure whether this applies if it is not accessible. Do you know?
I don't.

Is a thumbnail a tool? I can open Wiska boxes with mine.

I've got a number of general purpose ABS/polycarbonate enclosures with large quarter-turn "screws" at the corners that can likewise be opened.

I've known traditional round JBs to be capable of having the lid turned enough to loosen the screw enough to then finish unscrewing it with fingers.


And yet I have had people insist to me that a lever is not a tool.
 
Is a thumbnail a tool? I can open Wiska boxes with mine. ... I've got a number of general purpose ABS/polycarbonate enclosures with large quarter-turn "screws" at the corners that can likewise be opened. ... I've known traditional round JBs to be capable of having the lid turned enough to loosen the screw enough to then finish unscrewing it with fingers.
Agreed, on all counts ... so who knows?!

Kind Regards, John
 
FWIW, my conclusion to date (always open to update because of new evidence).

If you want something which definitely complies with 526.3(vi) then you can go and buy a Wagobox + the "correct" connectors, or an Ashley J8xx, or the LINE product above, or any other product where the maker claims BS 5733 MF compliance.

If you want a bit more flexibility then IMO you could, for example, use different MF-type connectors inside a Wagobox (the nature of the LINE enclosure shows that tailored recesses for, or close restraint of, the connectors themselves cannot be a requirement).

Or you could use any MF connectors inside any generally compliant enclosure where choc-block (for example) would be OK, as long as you de-rate the connectors and provide cable restraint.

Clearly the "a la carte" approach would not be compliant with 526.3(vi), but you could still issue a valid EIC by documenting it as a departure. Given what we now know of the varied approaches to BS 5733 MF compliance I would have no problem in declaring that in I had exercised reasonable skill and care when carrying out the "design and construction" of the junction box and to the best of my knowledge and belief the resulting degree of safety of it was not less than that which would be obtained by compliance with the Regulations.

If this is OK

upload_2017-12-4_11-24-37.png


then so is this:

upload_2017-12-4_11-24-52.png
 

Attachments

  • upload_2017-12-4_11-18-34.png
    upload_2017-12-4_11-18-34.png
    594.1 KB · Views: 307
  • upload_2017-12-4_11-18-54.png
    upload_2017-12-4_11-18-54.png
    346.2 KB · Views: 292
  • upload_2017-12-4_11-20-47.png
    upload_2017-12-4_11-20-47.png
    586.2 KB · Views: 316
  • upload_2017-12-4_11-22-26.png
    upload_2017-12-4_11-22-26.png
    587.1 KB · Views: 308