Not here - but then in fairness it's a cable size which has never been stocked here.As has been said, I don't think it was all that uncommon in the early days of (low-powered) electric showers.
Not here - but then in fairness it's a cable size which has never been stocked here.As has been said, I don't think it was all that uncommon in the early days of (low-powered) electric showers.
Not here - wholesalers never stocked it here.It was very common in the days of the first electric showers, which were often sub 7kW. I have seen loads of shower circuits run in 4 Milli and installed by Norweb (as was then).
Many were Dolphin Showers, installed in the 70s. Sometimes they had a Dolphin shower enclosure ( you had to have a bob or two), or more often installed over the bath.
Loads of showers were done in 4mm2 in the early 80s. Southern Electric used to do them, in 4 mm2. Always finding them.4 square is hardly a common size for a shower. In fact I would suggest that it's vanishingly rare to come across.
But you aren't in the UK (or are you?). Probably its not stocked in Sri Lanka, or Congo either....Not here - wholesalers never stocked it here.
I thought '4 square' is a a typical ceilidh dance.4 square is hardly a common size for a shower. In fact I would suggest that it's vanishingly rare to come across.
Does that really qualify as "C1" ?.... I'll go further and say in my experience; a 10.5KW running on 4.0mm² is in the top 5 C1's on EICRs.
I would say no, unless the fuse/MCB/RCBO had been modified, however if we look at the chart, ref 100 which is normal, 27 amp is the rating, so only ref C would allow the use of a 32 amp MCB.Does that really qualify as "C1" ?
Having encountered many 10.KW showers on B32's or 30 or 35A fuses and 4.0mm² cable which seem to be running correctly without any apparent damage, then no I don't believe it's a C1, in fact when there really is no damage I could almost see the justification for a C3. However I think it's fair to say they have only seen them as C1'sDoes that really qualify as "C1" ?
You've moved the goalpost slightly, by now talking about 10.5 kw Showers and 4mm² cable "protected by B32s or 30/35A fuses", but, even in that situation, I personally still cannot see how it could possibly qualify as C1, and might well struggle to regard it as C2 - as you say, C3 might be appropriate.Having encountered many 10.KW showers on B32's or 30 or 35A fuses and 4.0mm² cable which seem to be running correctly without any apparent damage, then no I don't believe it's a C1, in fact when there really is no damage I could almost see the justification for a C3. However I think it's fair to say they have only seen them as C1's
Per what I've just written to Sunray, do you really believe that any of the scenarios being discussed constitute a "potential danger", hence deserving even a C2 (let alone a C1 !).I can see both sides for code C1 and code C2, personally I would code it as code C2, as any codes C1 need addressing immediately.... . So 8 kW = 35 amp, so in the main a 32 amp MCB will hold for long enough to have a shower, but the next size down is 25 amps, or 5.7 kW, and it is unlikely even a 7.5 kW shower (32 amp) will hold long enough to complete one's shower.cable 'at any danger' - since, as I recently wrote, it is deemed to be able to carry about 41.
Bear in mind this ECO system cycling aimlessly around the random settings is potentially running at peaks of something like 25KWh of gas power.As to a combi boiler even more problems, the Bosch on in parent's house had two options, eco off or on. With the eco off, the shower worked OK, but with eco on, the shower would start cold, get hot, then go cold again, then finally hot again. But, with eco off using all other taps they had to be full on, or the boiler would not fire up.
I haven't moved anything, the thread had moved to showers on 4mm² cable, further I'm basically saying the same thing as you. Sadly the opinions of the EICR inspectors is generally based on a work generation scheme and marking something as C1 is more likely to result in additional profit than marking as C3You've moved the goalpost slightly, by now talking about 10.5 kw Showers and 4mm² cable "protected by B32s or 30/35A fuses", but, even in that situation, I personally still cannot see how it could possibly qualify as C1, and might well struggle to regard it as C2 - as you say, C3 might be appropriate.
"10.5 kW" showers are invariably 10.5 kW at 240 V, which equates to about 41.9 A at 230V
Method C 4mm² T+E has a CCC of 37A. It would be deemed to be 'safe' if it were protected by a hypothetical 37A MCB, and by virtue of the spec of such devices, that means that the cable would be deemed to be 'safe' (come to no harm) with a continuous current 'for ever' of about 41.8 A, and 'safe'with a current of about 53,6 A flowing for an hour.
The situation you describe would, strictly speaking, be non-compliant with BS7671 on at least two counts (ib>In and In>Iz), which might well be considered to justify a C3 - but, in view of what I've written in the previous paragraph, I would not personally regard the situation you describe as even 'potentially dangerous' - so not even a C2, let alone C1
It did but, if I recall correctly, not with any mention of the rating of the circuit's protective device.I haven't moved anything, the thread had moved to showers on 4mm² cable ...
As you say (and as above) we seem to basically agree. If they could not reasonably justify the C1 (and, as above, I can't see how they could), and if the CI were given for the reason you suggest, then might that not be a criminal offence, since it sounds like 'fraud' to me ?, further I'm basically saying the same thing as you. Sadly the opinions of the EICR inspectors is generally based on a work generation scheme and marking something as C1 is more likely to result in additional profit than marking as C3
Although I agree with this, there are no strict rules on the definitions and as everything is referenced to something which in iself has no legal standing the whole thing is on a sticky wicket.It did but, if I recall correctly, not with any mention of the rating of the circuit's protective device.
However, it doesn't really make much difference to what I have said. If the circuit were protected by, say, a 40 A OPD, the (modest) non-compliances would be slightly different, but my bottom-line view would be unchanged - that to have a load of about 41.9 A fed via 4mm² (Method C) cable (with any OPD) is not going to introduce any significant 'potential danger' - hence, to my humble mind, not even C2, let alone C1
As you say (and as above) we seem to basically agree. If they could not reasonably justify the C1 (and, as above, I can't see how they could), and if the CI were given for the reason you suggest, then might that not be a criminal offence, since it sounds like 'fraud' to me ?