However, regardless of what I was thinking (or not thinking!) when I wrote in that other thread, does it remain your view that (if one is concerned about 'current ratings' of connectors) it would be 'OK' to use a 20A-rated connector i a 32A OPD-protected ring final "because the reg for ring finals only requires the cable to have a (minimum) CCC of 20A?
If so, as I said, the regs obviously do not say that the CCC must not be above 20A, and would be happy with a current up to the actual cable CCC (possibly 27A) to flow (potentially 'continuously') - which is why, as I've said, I think some people might question the acceptability of a 20A-rated question.
In fact, on reflection, it is (strictly speaking) actually even 'less simple' than I previously suggested
. Although. in a ring final, the regs allow a cable with a CCC as low as 20A to be protected by a 32A OPD, the reg (explicitly) does
not allow a situation in which current in part of the cable is 'likely to exceed its CCC for long periods' - so, if the CCC actually is 20A, then a 20A-rated connector would seem fine. However, if, as is very possible, the CCC of the cable actually is 27A (in which case the reg would be happy for 27A to flow continuously in part of the cable), those people I've been talking about might suggest that the rating of the connector ought to be 'at least 27A' (not 'at least the rating of the OPD, which is what was previously suggested - although, in practice ≥27A obviously would mean a 32A OPD!).
Kind Regards, John