I have no need to measure the flows. I used thermometers. As long as the boiler had its minimum flow through the heat exchanger to cope with 40kW that is the only flow that really mattered as the boiler was fully protected.Why dont you chuck in some DRV and control stations and actually measure the flows, should be a laugh if not educational.
Please read what I wrote before you type. The header is 28mm. One shunt pump serving the header and two smart pumps on two heating circuits. The shut pump is a Grundfos and has a three speeds like all others.One 22mm pipe cannot supply 3 x pumps.
The boiler pump (Shunt pump) serves the header only or should, the 2 heating pumps are supplied from the header, or should be
How did you adjust the Intergas pump.
Your analogy of the car is not valid.If a boiler modulates, as long as it has the minimum flow through the heat exchanger the maker states, then an "oversized" boiler will modulate down pretty quickly to an applicable rate after giving a rapid heat up from cold. It is like having a large engine in a car. Most of the time only fraction of the power is used - it takes only 20hp to propel a large car at 70mph along an Mway, yet the engine may be rated 100hp. The power available can be used for acceleration, like the rapid heatup in a large boiler.
On start up on cold the system will take all the boiler can throw at it until warm. In the analogy of the oversized car engine and the extra power used for acceleration. The spare power in the boiler is used for rapid warm up.Your analogy of the car is not valid.If a boiler modulates, as long as it has the minimum flow through the heat exchanger the maker states, then an "oversized" boiler will modulate down pretty quickly to an applicable rate after giving a rapid heat up from cold. It is like having a large engine in a car. Most of the time only fraction of the power is used - it takes only 20hp to propel a large car at 70mph along an Mway, yet the engine may be rated 100hp. The power available can be used for acceleration, like the rapid heatup in a large boiler.
A boiler's output is limited by the capacity of the radiators to absorb the heat produced.
They all modulate down quite quickly.If you put 40kW into a system with only 10kW of rads the return temperature will rise so fast that the boiler will be unable to modulate down quickly enough.
This problem was seen by the makers and they amended their control systems to suit. The Intergas modulates UP. It starts up on the lowest setting.There are many examples of this on this forum (mainly with combi boilers) and the solution has always been to reduce the heating output so it is comparable to the total capacity of the radiators.
The flow pipe from the boiler to the header gets hot, the part of the header to the two heating circuit' tees gets hot and the smart pumps pump all the heat out of the header into the heating circuits. The header is short circuited. When the smart pumps wind down the flow runs right through the header. I have explained this a few times to you.So there is flow through the header, how come it doesn't get hot
I am pretty sure it is a Grundfos pump. I will check tomorrow. It is three speed job for sure.
No. Read the label on the pump. duh! What the hell is an " ol' muckka"? No, don't reply. It is best you do not reply to anything.I am pretty sure it is a Grundfos pump. I will check tomorrow. It is three speed job for sure.
What were you saying about reading the manual?
The flow pipe from the boiler to the header gets hot, the part of the header to the two heating circuit' tees gets hot and the smart pumps pump all the heat out of the header into the heating circuits. The header is short circuited. When the smart pumps wind down the flow runs right through the header. I have explained this a few times to you.So there is flow through the header, how come it doesn't get hot
I am pretty sure it is a Grundfos pump. I will check tomorrow. It is a three speed job for sure.
It is clear you do not know how this is setup. Read what I wrote.The flow pipe from the boiler to the header gets hot, the part of the header to the two heating circuit' tees gets hot and the smart pumps pump all the heat out of the header into the heating circuits. The header is short circuited. When the smart pumps wind down the flow runs right through the header. I have explained this a few times to you.So there is flow through the header, how come it doesn't get hot
I am pretty sure it is a Grundfos pump. I will check tomorrow. It is a three speed job for sure.
Repeat.
In that case explain how 3 pumps can be satisfied with 1 22mm pipe and the resistance from the boiler.
The heating circuits are balanced and the smart pumps on the lowest. When startup from cold the heat from the boiler flow goes through the two heating circuits. The heating returns run back to the header and mainly run into the return. most flow is from the boiler into one end of the header, through the two smart pumps into the heating circuits and back into the end of the header and into the boiler forming that loop. The header is primarily by-passed.You can't have it both ways, and in every case the heating must be circulating through the header
You got the first part right. But 1.5 m/s is a maximum. Most systems are designed for less than that, say 1 m/s .The heat carrying capacity of a pipe is limited by the maximum acceptable velocity for noise reasons. This is generally taken as 1.5 m/s.
I can guess where you lifted those figures from!15mm = 18.1kW;
22mm = 40.2kW;
28mm = 67.5 kW.
Don't you mean the secondaries?Now for the low-loss header. The ballpark to size the header is 3 times the area of the boiler's primaries pipe size into the header.
13kw is somewhere between the 1 m/s and 1.5 m/s. Borderline but 15mm pipe can do it.You got the first part right. But 1.5 m/s is a maximum. Most systems are designed for less than that, say 1 m/s .The heat carrying capacity of a pipe is limited by the maximum acceptable velocity for noise reasons. This is generally taken as 1.5 m/s.
I can guess where you lifted those figures from!15mm = 18.1kW;
22mm = 40.2kW;
28mm = 67.5 kW.
For a more normal max velocity of 1 m/s the capacities are:
15 mm: 12.07 kW
22 mm: 26.8 kW
28 mm: 45 kW
No. Primaries. In a fixed output boiler and constant flows, the boiler will be sized for the whole heating load. The heating circuit pipes will be sized to suit. The primaries should deliver all the output from the boiler. In short, the primaries will be bigger than Heating circuit pipes. The primaries will match the heating circuits. Same in, same out. If the heating circuits are larger than the boiler's output the header should be upsized to a buffer tank, then boiler is too small and heat storage is needed.Now for the low-loss header. The ballpark to size the header is 3 times the area of the boiler's primaries pipe size into the header.
Don't you mean the secondaries?
Only just noticed that clanger! It should be three times the diameter, i.e nine times the area, so the velocity through the header is only one ninth of that through the secondaries.AlexCarp said:Now for the low-loss header. The ballpark to size the header is 3 times the area of the boiler's primaries? (secondary) pipe size into the header.
No ballpark is using area. With 22mm primaries the header would be 66mm taking diameter.Only just noticed that clanger! It should be three times the diameter, i.e nine times the area, so the velocity through the header is only one ninth of that through the secondaries.AlexCarp said:Now for the low-loss header. The ballpark to size the header is 3 times the area of the boiler's primaries? (secondary) pipe size into the header.
The reason I queried 'primaries' is that it's the pressure drop between secondary connections which have to be minimised.
Exactly. The heating circuits and primary circuit must operate independently of each other with no influence to each other.The objective is to create a neutral point between the secondary connections.