I haven't read all yet....
Boiler is too big. Get a correct sized boiler and fit zone valves and pump. Simple.
Daniel.
Boiler is too big. Get a correct sized boiler and fit zone valves and pump. Simple.
Daniel.
So all combis are too big then. Well do not write tripe then. Why do these people feel compelled to comment on something they know nothing about?I haven't read all yet....
Boiler is too big. Get a correct sized boiler and fit zone valves and pump. Simple.
Daniel.
[
Exactly. The heating circuits and primary circuit must operate independently of each other with no influence to each other.
The heat carrying capacity of a pipe is limited by the maximum acceptable velocity for noise reasons. This is generally taken as 1.5 m/s. With a temperature drop across the system taken as 20C for a condensing boiler, the carrying capacity of:
15mm = 18.1kW;
22mm = 40.2kW;
28mm = 67.5 kW.
These figures are maximum and may need reducing to account frictional resistance and pump head.
Where did you get that from?No ballpark is using area.
?......I used the content to fit a system in an average semi.
Yes, that's one of the big problems with combis - you either have crap DHW or a grossly oversized boiler for CH, or both.Boiler is too big.
That doesn't actually solve the problem. The heat demand is highly variable, and so the required flow rate round the CH circuit(s) varies. So there are mutually incompatible requirements for a minimum flow rate round the boiler, and a variable flow rate round the CH circuit(s).Get a correct sized boiler and fit zone valves and pump.
Yes. That is why 22m pipe was used.Have you any idea the of the noise these velocity rates will impose within the pipework?
That is ballpark and many use that.As for header diameter being '3 Times the diameter' then it will depend upon application ,
Can you tell us please? Try Google if you like. You have never given ANTHING of any use whatsoever. I would not let you near my house.maybe you can tell me the required header size for a 100 kw load @ 0.2 m/s velocity rate???
I did it and tested it. It works very well indeed. You make things up.And neither it seems do you.
A knowledgeable and intelligent installer would do no such thing. Please understand heating or stick to drains.Now I read it all.?......I used the content to fit a system in an average semi.
A good installer will fit a good sized vaillant system boiler with bypass built-in, 2 x zone valves for upstair and downstair radiators with TRV fitted, programable room thermostat, Unvented cylinder for hot water.