No, 200 ohms isn't a pass. As a means of earthing the rod needs to be less than 21 ohms with respect to mother earth (figure from the front of the on site guide.)From meter you take lead to rod rather than DNO's earth. As already said it will read a little on high side but anything under 200 ohms is a pass when using an RCD anyway so good enough.
We are not talking TT supplies here, we are talking means of earthing for a Terra system (TN-S).
GN3 allows us to use a normal EFLI tester for a TT system. For a means of earthing for a Terra system the 3 or 4 lead tester needs to be used.