Both.
Regardless, what about overcurrent protection?
Regardless, what about overcurrent protection?
I don't really get that. If it was a response to my first question, that would mean that you were agreeing with me that "ADS" does not encompass overcurrent protection. If it's a response to my second question, you're merely telling me that "ADS" was never called "EEBADS" in your machinery world.Both.
I don't understand your point. An OPD will respond to an overcurrent purely on the basis of the current - e.g. a Type B MCB will operate within an hour at 1.45In - and that's not affected by the 'source impedance'. If the source impedance is so high that the current in the circuit never gets high enough to cause an OPD to operate, then there is no need for an OPD to operate.Regardless, what about overcurrent protection?
Possibly, possibly not. We've debated this previously.If the source impedance is so high that the current in the circuit never gets high enough to cause an OPD to operate, then there is no need for an OPD to operate.
I don't recall that. As I see it, if the OPD is appropriately rated to satisfactorily protect the cable, then that's it. If aspects of the circuit (or source) are such that it's impossible for an overload current to get high enough to damage the cable (hence also not high enough to make an OPD operate), then I don't see what the issue would be.Possibly, possibly not. We've debated this previously.
That seems an awful lot of money for a 100A C/O switch, a 40A RCD and a couple of indicator lights in a polystyrene box (and that plastic box may not be compliant with current Wiring Regs)... inc. VAT: £255.00
That's what I'd have thought.As I see it, if the OPD is appropriately rated to satisfactorily protect the cable, then that's it.
I'm not really sure what you're saying here. Are you talking about the magnetic tripping failing to operate at a current which should cause it to operate, or a fault of sufficiently high (i.e. not 'negligible') impedance that the fault current is below the magnetic trip threshold? In either case, I'm not really sure what you are suggesting one can do about it.That's what I'd have thought. ... There seems to be this concern that in the event of a fault, the magnetic trip may not operate. If the supply impedance is too high for that, then the effect is similar to an overload rather than a fault - and the OPD will operate (or not) according to the current present.
In terms of the sort of genny likely to be used domestically, in my experience the usual response to an overload is for it to stop!Then we come to the issue of what happens to the genny if we overload it ...
I suspect that a problem with that could be that small gennys are simply not capable of supplying even remotely high currents (whether fault currents or otherwise). If that is the case, then installing an MCB which would trip magnetically at the maximum current the genny was capable of supplying would seriously restrict the continuous current that could be supplied during normal operation.If the Z of the genny is too high for a 32A MCB to trip on a fault then fit an MCB on the genny output that will trip on the fault current that the Z of the genny will allow to flow through the fault. The genny may already have one already fitted.
the MCB is fitted between generator and the change over switch and would not affect normal operationrestrict the continuous current that could be supplied during normal operation.
Exactly. That's what I said a while back, as far as overload protect (of cables) is concerned. As you say, the tables we use effectively indicate what cable is 'safe' with what OPD. If aspects of the supply or installation are such that it is impossible for the current to become high enough to cause the OPD to operate, then that's fine - it simply means that the cable is always 'safe' and doesn't actually need the protection of an OPD.... Either the current is high enough that sooner or later the OPD will trip, or it's not high enough for that. In either case, the tables of cable size/installation method/OPD type/etc cater for that - the overload tripping characteristics of the OPD are factored into the permissible combinations such that no dangerous situation downstream of the OPD will occur. Neither the OPD nor the cables care whether the current is limited by a large Zs or a large Zload - current is current.
I don't understand. The current being supplied 'during normal (i.e. non-fault) operation' (from genny supply) would have to pass through that MCB.the MCB is fitted between generator and the change over switch and would not affect normal operation
Indeed. However, as I said, if the maximum current the genny can supply is very limited, then an MCB chosen to magnetically trip at that current might restrict how much current could be supplied continuously during 'normal' (genny-supplied) operation.OK I took normal to be from the mains. The MCB between genny and changeover is selected to be one that wil trip magnettically on what ever current will flow from the genny, into a dead short and then back to the genny.