Believe me, I have carried out many reports where landlords have had a pass previously and I have failed the installation on several (serious)counts. These have mainly been due to tampering but sometimes due to points missed in the previous inspection.
And on how many inspections have you found faults missed by the previous inspection when you have done the previous inspection ?
And how many faults would not have been picked up by IR testing at a reduced voltage rather than 500V ?
He is correct to state that unnecessary dismantling has the potential to introduce faults and should be avoided.
Thank you for confirming that. Ie, that dismantling is not a zero risk action as some would claim.
That said, insulation resistance testing at 330V DC is daft. 500V DC is the correct voltage. It is, after all, a stress test.
That is obviously strictly true, but I wouldn't mind betting that it's incredibly rare to come across faults due to marginal insulation breakdown which would be apparent at 500V but undetected at 330V (or even lower).
I am aware of one situation where exactly that can happen - and that's where "surge protector" type devices are present. Indeed, I have a couple of 4way 'surge protected' extension leads that were thrown out from work because they "failed" PAT - testing at 500V made the protection devices conduct and present a low IR.
They also have (had) a neon between live and earth, but that's a separate debate.
Other than that, it is highly unlikely that testing at 500V will show defects that won't also show at 330V (or 250V) - at least for a modern installation with modern PVC insulated cables, and nothing subjected to adverse conditions. I could see potential for older installations with (eg) cotton/rubber cables and so on.
As I see it, to comply completely with the guidelines, IR testing should be at 500V. But also to comply with the guidelines, IR testing should not be at above 330V so as to avoid unnecessary dismantling.
Given that I've tested the RCBO devices in use and shown that they don't affect an IR reading*, it comes down to which has the higher risk :
1) Introducing a fault through 'unnecessary' dismantling
2) Missing a fault that would be detected at 500V but not 330V
No-one has come up with any convincing argument for 2 being higher than 1 - accusing anyone who considers 1 to be irrational is not a convincing argument, in fact it's not an argument at all.
* As mentioned in my earlier post, they do one way round, but not the other.