Well, even that one is a good start for discussion. As 415.2 effectively says, in the case of a bathroom, one has to comply with 701.415.2 as well as 415.2 itself, and 701.415.2 appears to explicity require connection of SB to "the terminal of the CPC".
It's not really that specific.
It says "Local SB shall be established
connecting together the terminals..." and, as has been agreed, 543 states what may be used for this purpose.
Apart from that, there are plenty of regs. which state something must be done in such a way but obviously do not apply when that thing is not required at all.
Main Bonding, for example, has very specific instructions about its connection but is not required if the part is not extraneous.
It certainly makes electrical sense to do it like that, but I'm still far from convinced that this is what the regs intended. If you are relying on 415.2.2 to make this (sensible) approach compliant, then please see below.
Hmmmm. It actually says "Where doubt exists about the effectiveness of supplementary equipotential bonding...", rather than "Where doubt exists about how well electrically connected e-c-ps are...". As I said, I would have thought that one can only "assess the effectiveness" of something which exists, and I really don't find it easy to interpret those above words as meaning that 415.2.2 can be used to decide whether SB may be omitted (in a location that does not yet have SB).
It is often the case that SB is not immediately visible as it does not have to be in the room.
Therefore a test is carried out to determine R≤50/Ia. It does not then matter what is achieving this desired result.
You are missing the main point that SB is to ensure touch voltage is below 50V so if it already is all is well.
I'm not sure I've ever thought about this before,
I am surprised.
but I'm having some difficulty in actually understanding the logic of the 'tests' described in 415.2.2, which relate specifically to the resistance between simultaneously touchable extraneous-c-ps and exposed-c-ps. I need to think about this, and may have more to say after I've thunk!
As above, it is to limit touch voltage to what is considered 'safe' i.e. 50V.
Therefore, if the installation (in the location) only has a touch voltage of, say, 25V then there is no need for supplementary (i.e. additional) bonding.
In the case of the OP there is only a lighting circuit and radiator pipe.
So R≤50/Ia = R≤50/30 = R≤1.66Ω
His measured resistance is 0.2Ω. 30x0.2 = 6V.
Whether this is because of the bonding he has seen in the airing cupboard or just the situation in the premises does not really matter.
[Just in case there is a 5A fuse and not 6A MCB (used in the example) I would point out that the conditions are similar; indeed, less onerous.]