I don't see the argument.Indeed, but your (415.2.2-based) argument would seem to apply even if satisfactory Main bonding was not present and/or 701.415.2(vi) was not satisfied (i.e. such that the regs seem to indicate that SB would be required), wouldn't they?
Main bonding should be checked whatever job is being done and should be compliant.
Were it not in place then the 415.2 tests would surely be equally relevant for SB but the situation should not arise.
As I said, because that is the arbitrary limit for omission of SB, albeit (effectively) impossible to ever be relevant like the 23kΩ limit for MB.That makes sense, but there is presumably some reason why they put the RCD Ia into that reg?
Yes, of course. That is why it is why SB is dependent upon it (test).I would imagine that satisfying the '415.2.2 test' when there is no RCD could quite easily be a struggle (particularly for a shower circuit), since it presumably requires a resistance between parts which is nearly 4.6 times lower than the 'maximum Zs' (currently) required of a circuit for ADS.