Even if the heat loss is as low as you think it is, you are not giving the system any help by having a boiler which has a minimum output 50% more than the total output of the rads. The boiler will be short cycling all the time, which is not efficient. The problem is exacerbated because the boiler starts at max output each time and has to modulate down to minimum, after which it turns off and waits over two minutes before restarting. It might be worth considering an increase in radiator output.
Are you sure that the walls of your house are unfilled cavity? Changing from unfilled cavity to the "best" option saves 3kW; and increasing loft insulation to "best" saves 2.1kW.
Which room thermostat do you have?
Yes, I am 100% with you D_Halisham. I've thought a lot about that. It would be a sensible course of action.
I started writing this thread from the perspective of lowering boiler output, as a stop gap to try to give the boiler a bit less stress, but the other way would be to increase emitter output as after all the discussion, it seems opportunity is limited on the current boiler front.
A new boiler that modulates to 6kw would also help a lot but funds are tightly stretched at present.
In the end, I've just replaced two faulty old imperial sized rads with Myson premier single panels, despite clearly seeing that more output would be useful. It was problematic enough for me dealing with adjusting widths (and pipe depths slightly) and having to cut the old olives off to fit new valves on all pipework for both old and new rads. Dealing with double panels would of needed to start again with the feeds and space in some areas like hallway and bedrooms is limited.
Also for time being, I've stuck with single panels because all the drop pipework on ground floor is beneath a laid laminate floor. And the boards run the wrong way on most rads as well, so removing a lot of laminate and then at least a few boards for each radiator seemed too make things just hard and disruptive. And then, unless doing every radiator in the house, downstairs will probably be significantly out of balance with upstairs... Maybe that wouldn't be so bad, as I prefer it a bit cooler in bedrooms....
We also like the minimal depth of the single panels, and they are used in every room.
But using your pointer, when we come to do some more work, maybe another rad underneath the window in the front lounge and a fan assisted plinth heater in the kitchen would help raise output a bit. There is presently no heat in the kitchen at all and it is pretty cold but there is no room to sit in there apart from a tiny small children's table sitting in the way of some cupboards (so it rarely bother that much)........
The bathroom towel rail does not heat the room sufficiently either, probably needs to be double size or more, so we could up some capacity there by changing it to a vert rad. I could see all that might raise things 2.7kw? So we'd be pushing over 10kw.
All the original walls are unfilled 100%, I've knocked a few holes in them for various things. 75mm cavity. There is a small 2 storey gable end extension to the kitchen and 3rd bedroom. There are bats in that cavity mid 1980s built. It is only about 3m x 1.9m (2 storey) so pretty small part of the overall property.
I use a Honeywell CM927. It does a good job of controlling the room temp, but I have had to change it from the 1min / 6 cycles per hour. It is set to 3 cycles, 4 minutes minimum.
Just for clarity: When I have been quoting burner cycle and rest times in here I have not been confusing it with the TPI on the CM927. All the burner cycling and gas rate measurements are before the actual temp is within 1.5C of the target temp, so before intervention from the CM927.
Thanks again for the pointers.
Ps. even though the boiler has operated like this since presumably being installed. With the set up we have now, TRVs upstairs and the CM927, mostly unfilled cavity walls, no floor insulation. Heat for 17 out of 24 hours most days, temps on 18.5 or 19.0C, our gas use is not horrific. Much, much lower than the SAP energy estimate anticipated when we bought.
Annual Gas use is about 13,500kwh per year. If you took off Hot Water, probably about 10,000 kwh space heating...
Edit: I will measure gas rate at the meter during the 2min 30 on cycles in the morning and see how close the overall rate is to minimum modulation. If it indicates a materially higher gas rate than minimum maybe there could something in getting it wound back to minimum range on CH....