A boiler will only condense if the system has been designed so the return temperature is low enough (<55C) for condensing to occur. If a condensing boiler has replaced a standard boiler, there is a good chance that it will only condense on rare occasions because the system was originally designed for a return temp of about 65C.
Nothing to do with working flat out.
A boiler will only condense if the system has been designed so the return temperature is low enough (<55C) for condensing to occur. If a condensing boiler has replaced a standard boiler, there is a good chance that it will only condense on rare occasions because the system was originally designed for a return temp of about 65C.
Ideal, don't 24kw combis have 19kw max heating output 24kw for dhw? the heating output is never as much as dhw. Then after the boiler figures out the output required from it it will modulate down to suit the load. So combis aren't oversized, but you need a minnimum (24kw) output on the hot water side to be able to provide acceptable hw rates. On most boilers you can set the load for the heating yourself...
That Chantelle doesn't seems very helpful, just likes to mouth off it seems.
Always remember, it takes more energy to put the heat into the water from cold. You want to heat it and keep it hot so a boiler chucking out 30kw say when all you need is 12kw will cycle which is inefficient. That's about my limit, need to learn more. Any answers to this will be appreciated, I promise not to tell you to get over yourselves or that your wrong
But your physics is assuming a differential of 11C at the boiler. If you are using a boiler designed for a 20C differential, the flow rate is approximately half; so the same 22mm pipe can now carry 32kW.Remember no more than 17.6kw down a a 22mm pipe, can't argue with physics
What is your evidence?Mine condenses plenty!
What is your evidence?Mine condenses plenty!
If you are getting a steady drip then only a minimal amount of condensing is taking place; the return temp will be about 55C. The amount of condensate (water) produced increases as the return temperature reduces. So a boiler running at 50/30 will produce more condensate and a higher output (kW) than one running at 75/55.The condensate pipe runs outside and into a surface water drain. When the boiler is on it emits a steady (almost non stop) drip. Admittedly I haven't sat and watched it for hours, but when the boiler is working hard (all radiators calling for heat, sometimes with HW being called at same time) then condensate is coming out the condensate pipe.
I read English Literature with a bit of computer programming and Anglo Saxon linguistics thrown in.
Reading and listening to the right people basically. That's why I hoover every bit of technical literature I can for the ccr