Ok that video was helpful, so you use a fuse so that the rcds/mcbs further downstream will trigger first if there's a fault on one of the circuits downstream so as to only shut off the faulty area rather than the whole thing. This would make it much easier to locate the source of any fault because the area that trips out would be more localised. If you used an RCD of the wrong type further upstream then that would cut off the whole circuit, as would an MCB but you could use maybe 100ma RCD but this doesn't seem necessary with because it's a SWA cable and any cable damage will result in everything going to earth and blowing the fuse. I'd say maybe an 80 amp fuse would be good for a 16mm cable that way the RCD or specific circuit MCB downstream CU in the cabin would trip before the fuse blows unless the swa cable got damaged in which case the fuse would blow before the cable meltedLook up "discrimination/selectivity" with relation to fuses, MCBs etc. Look at the time/current trip curves for MCBs and various fuse types. You should then be able to work out why a fuse is being suggested as the upstream device.
It's nigh on impossible to accidentally damage an SWA in the way you describe - that's the main point of earthing the armour.