At least you didn't have to spend all day waiting in a queue at the 'border'!I was in the EU three times today. It's a wonder I didn't get CE marked.
At least you didn't have to spend all day waiting in a queue at the 'border'!I was in the EU three times today. It's a wonder I didn't get CE marked.
Funny that... IR heaters and 13A plugs burning out.One of my regular calls is to a factory which uses infra red heaters (3kw) plugged in to 13 amp sockets, pays for my wine
I don't think there's a lot wrong with the "BS1363 plug/socket system" (the Standard), so that a lot of the issue is presumably that some of the products are not necessarily BS1363-compliant.It would appear the BS1363 plug/socket system is not fit for purpose. Time for a change perhaps!
Indeed, and I think that 'someone' was me.As someone above mentioned, there is probably no issue with brand new parts. However as time goes by, the plug pins and the socket spring contacts tarnish and their resistance goes up, out of spec. I have experienced this back when I was running loop resistance checks on my house, using a 13A plug connected to the tester. None of the readings was in spec, they were all over the place. The only way to get a good reading was to insert the plug about twenty times to remove the tarnish.
I don't think there's a lot wrong with the "BS1363 plug/socket system" (the Standard), so that a lot of the issue is presumably that some of the products are not necessarily BS1363-compliant.
They are, in many fields, and give a guide, but they are rarely able to very effectively reproduce actually in-service conditions.Mmm. Artificial aging techniques are available for testing.
That could be true.But I doubt anyone cares enough.
That makes some sense. However, as winston has said (and as witness what resulted in this particular thread) it seems that the issue is quite often associated with the fuse, rather than the pins.On the other hand I have seen plugs with plated pins that may be more resistant to tarnish. Not sure how well that works on the socket side though.
Yes but, as I implied, if the plugs/sockets had been truly BS1363-compliant, he may not have needed to change to 15A ones.Sunray’s experience seems to suggest there is as the problem went away once he had changed to 15a plug/sockets.
That certainly often seems to be the case, but the requirements of the Standard should really address that.I believe the problems are due to the fuse or it’s contacts heating up.
The reality is that the repercussions of the change that you think 'it may be time for' would render the change almost unthinkable in the UK, as it is - unless you would be happy to see unfused plugs on 32A circuits (of which there must currently be countless millions in the UK).As I said perhaps it is time to change. Overseas systems without fuses in the plugs don’t seem to have over heating problems.
You seem to be implying that the 'ratings' (of cables, connectors and accessories etc.) we work with are not intended to relate to continuous usage, and I'm not sure that is necessarily the case.Very easy: When using equipment for continuous loads like a electric heater in a cold room for more than a couple of hours. One MOST derate any wire or extension cords by 20%. ... The same for a charging an EV. It is actually in the standards: IEC 61439-1:2020 Appendix L4.2
All true, but I very much doubt taht either of those factors, per se, have had any appreciable effect on heat production.The 13A plug and socket was designed for heating homes at end of WW2 however some changes have likely derated the system.
1) reducing metal in pins to allow finger guards.
2) move to smaller metric cable.
Again, all theoretically true. However, I don't think that fuses usually get hot enough to cause any harm - when fuse-related overheating occurs in a BS1363 plug or FCU, it seems that it is almost always due to poor connections, not to the fuse per se.But any fuse produces heat, and there needs to be a means to get rid of the heat, black plugs are better than white, and the larger the better to dissipate heat.
Maybe - but in the real world, they sometimes aren't, or can't, be - and the actual heat-producing items, particularly the fuses, obviously cannot themselves be 'exposed' in free air!Flex, and plugs should be in free air.