I need to put a supply in for a 22A FLC 3ph motor (fan unit). Cable length is about 100m.
I am not sure on the motor connections as inside the terminal box there is just the 3 line conductors, and no options to fit star/delta links.
What would be the maximum permissible volt drop on start up without it causing problems, I believe 15% is OK?
Based on this, 3.8mV/A/m 10mm cable will give me a 40V drop (approx.) at 100m and with a start up current of 120A.
Thoughts?