As a theoretical question, the answer would be "It depends on lots of thing".Based on this - would you still say 20 or 16 mcb to replace the 32??
In your case just instal the lowest rated MCB that will let your appliances work properly.
As a theoretical question, the answer would be "It depends on lots of thing".Based on this - would you still say 20 or 16 mcb to replace the 32??
Words fail me...The mcb is to protect the cable. The current carrying capacity of a 2.5 cable is 24A. The closest mcb size to that is 20A. If you linked the socket and the microwave with a 2.5 cable you have made it from a 2.5 to 5.0mm2. Do you know what I mean? The reason a ring main can go on a 32A is because it is 2 x 2.5 cables making it 5mm2 in total. Because it's been split to single 2.5s it can only carry 24A maximum. So yes it needs to go on a 20A unless you put a 2.5 to link the two cables. With the loadings you have statd the cable isn't going to be overloaded and is fine. But I'd put a 20A mcb in then the circuit is covered
And yes I forgot to mention sorry - that from consumer unit - there’s a 4 or 6mm cable for about 1 metre that then splits off into
the 2.5 kitchen ring cable
The 2.5 radial oven
YOU ARE A "FULLY QUALIFIED ELECTRICIAN" - YOU ARE NOT SUPPOSED TO JUST GUESS!I wasn't far off with 24A haha it was a good guess.
Possibly because of the mistakes and dubious understanding of basic principles shown by the highlighted parts in this?:Why do words fail you detlefschmitz
The mcb is to protect the cable. The current carrying capacity of a 2.5 cable is 24A. The closest mcb size to that is 20A. If you linked the socket and the microwave with a 2.5 cable you have made it from a 2.5 to 5.0mm2. Do you know what I mean? The reason a ring main can go on a 32A is because it is 2 x 2.5 cables making it 5mm2 in total. Because it's been split to single 2.5s it can only carry 24A maximum. So yes it needs to go on a 20A unless you put a 2.5 to link the two cables. With the loadings you have statd the cable isn't going to be overloaded and is fine. But I'd put a 20A mcb in then the circuit is covered
No, it isn't.I know 2.5 is a 20A maximum when it's own.
No, it isn't.That's the most important thing.
Yes it can.Yes i could look up the exact Amps in the regs book but I know it can't go on a breaker on its own over 20A
Errr - because it isn't?so why do I need to look when that's fact?
Very true - but the maximum CCC of the cable most commonly used for one of the most commonly inatalled circuits in domestic installations???No fully qualified electrician knows every single regulation off by heart