It's CCC in Method C is 27A, therefore ... any one less than that will be compliant.So what mcb would you put a single 2.5 on?
It's CCC in Method C is 27A, therefore ... any one less than that will be compliant.So what mcb would you put a single 2.5 on?
You should get out more:So they are but I'd say most standard practice is to use a 20A. I've never come across a 25A radial circuit before
There are (probably) millions of single lengths of 2.5mm² installed on 32A breakers.It's CCC in Method C is 27A, therefore ... any one less than that will be compliant.So what mcb would you put a single 2.5 on?
You really should get out more!I can honestly say I've never known anyone use a 25A
He didn't tell you that it also applies to cables buried in chases in walls and/or plastered over?I took comfort from his original explanation:
“ ..
The rating of 27A that you were given earlier is correct, but only when the cable is run clipped directly to the surface of a wall. Not the most attractive way of running a cable, and not the way that the cabling in question is run in your house to your utility/kitchen areas.”