I'd prefer the solution of doing away with ring finals.Simple solution.....Do not install double sockets. Install only singles in areas where over loading may be possible.
I'm confused. The argument you are presenting would mean that, with some provisos, it is OK to have a short (<3m) radial circuit supplying a single double socket, wired in 2.5mm² cable(installation method A/100/102), or even 1.5mm² if 'clipped direct', protected by a 32A (or even 50A) MCB, on the basis that the double socket 'cannot' represent more than a 20A load, and that the combined In of the fuses in associated plugs 'cannot' exceed 20A. Do you think that "every single electrician who has signed an EIC/MWC/EIC/EICR since 1946" would agree with that?I'm not the only one who disagrees with you. To the list you can add the members of JPEL/64 and its predecessors, and every single electrician who has signed an EIC/MWC/EIC/EICR since 1946....
The same problem would arise with a 4mm² 32A radial. The problem would only go away if 'double 13A sockets' which could not safely handly 2 x 13A loads were to be banned. In the meantime, Bernard's solution would be the only foolproof one.I'd prefer the solution of doing away with ring finals.Simple solution.....Do not install double sockets. Install only singles in areas where over loading may be possible.
Of course then we get onto the fact that BS1363 does not require socket doublers to be fused....imple solution.....Do not install double sockets. Install only singles in areas where over loading may be possible.
If they don't then they should not be signing off installations which have spurs etc like that, should they.Do you think that "every single electrician who has signed an EIC/MWC/EIC/EICR since 1946" would agree with that?
The accessory problem would remain, but all of the circuit protection ones would disappear.The same problem would arise with a 4mm² 32A radial.
That's what I'd be interested to hear from those in question....If they don't then they should not be signing off installations which have spurs etc like that, should they.Do you think that "every single electrician who has signed an EIC/MWC/EIC/EICR since 1946" would agree with that?
Agreed. However, Bernard's comment/suggestion presumably related to the 'accessory problem', since use of two single sockets rather than one double would (a) be non-compliant in the situation we've been discussing and (b) would actually kill your argument about circuit protection (since there would then be no doubt that we were talking about an Ib and 'total In' of 26A, not 20A).The accessory problem would remain, but all of the circuit protection ones would disappear.The same problem would arise with a 4mm² 32A radial.
The 200A fuse (or 20,000A, come to that!) would be OK for BAS's argument, but the 1mm² cable would not be, since, per his theory, it would be protected by fuses with 20A's worth of In at t'other end - but, yes, it would seem that 1.5mm² cable supplied directly from Henleys on the meter tails might satisfy him!Bas must be happy with that because he doesn't understand 433.2.2.so folks, what you you think about a radial circuit supplying just one double socket, 2.8m in length, run in 1.5mm² cable (clipped direct) protected by a 50A MCB? Is everyone happy that such an arrangement is compliant and 'satisfactory'?Why not a 200A fuse and 1mm if you believe BAS's bizarre interpretations.
Can you show that 1.5mm² is afforded fault protection by a 50A MCB?- or are you assuming that an RCD is present in the circuit?Can you show that 1.5mm² is afforded fault protection by the service fuse?
No, but nor can I show that it is not.Can you show that 1.5mm² is afforded fault protection by a 50A MCB?-
Not much use with a L-N fault.or are you assuming that an RCD is present in the circuit?
That makes two of us, then - but you seemed previously to be happy to assume that it would be OK with 2.5mm².No, but nor can I show that it is not. i.e. I have not done the calculations.Can you show that 1.5mm² is afforded fault protection by a 50A MCB?-
Never assumeTBH, I have not done them for 2.5mm² on a 30/32A device either - I'm assuming that given 433.2/.3/434 and the fact that spurs like that are permitted, someone has.