Sorry, John - I'm really struggling to understand how one could (or would wish to) not use the presence of BS 1362 overload protection devices to show that the cable had overload protection...However, my point is that one could use the presence of the BS1362 fuse(s) (certainly for a single socket, possibly/probably for a double one) to indicate that that the spur cable was "not likely to carry overload current".
But you can't, you don't need to and you would never want to - it is those BS 1362 fuses which give you your overload protection...If one did that, then, provided fault protection was OK, there would (per regs) be no need for any overload protection, hence 433.2.2 (number hasn't changed), with its 3m limit, would become irrelevant.
Well in that example it isn't, and that is the whole thrust of this topic - a 20A radial using 2.5mm² cable had damn well better be protected from overload just like a 2.5mm² spur from a ring final by the fuses in the plug(s) or FCU, and from fault currents by the upstream device. And in the absence of tailored adiabatic calculations, that fault protection requires, inter alia, that the cable be no more than 3m long.As for the fault protection, I need to think about what you've said but, on the face of it, I can't see why achieving an adequate degree of fault protection should be any more difficult in this situation than it is for any other circuit (e.g. a 20A socket radial) using 2.5mm² cable.